Discuss EICR readings in the UK Electrical Forum area at ElectriciansForums.net

J

joehat

Hi all

Done an EICR today and on one light circuit my zs tests was coming with error so got the 2 poor tester out, and I'm getting 50v between 230 l-n and 50v l-e

Checked all switches and light fittings Ect, nothing obvious, property 13 years old,

I've checked all downstairs and seems to be near the cu as same readings on all, so gonna find out when next their which one the 1st light is, and then test the earth after that to the other lights and I then I'll know more where the issue is.

Would you say this is either a poor connection hidden somewhere or a screw through a cable Ect , any ideas.
 
I did code it c2 and moved onto rcd side as that was a fix to make it safer for now, and Because I've been asked to go back and Find the problem that's why
 
Oh that that it's a good customer of mine and like to go the extra mile. Anyone else I would just code and go back if asked Ect ( I did get offered more money, but it's local and a good customer so an extra hour isn't the end of the world, it's give me a good rep.
 
Hi all

Done an EICR today and on one light circuit my zs tests was coming with error so got the 2 poor tester out, and I'm getting 50v between 230 l-n and 50v l-e

Checked all switches and light fittings Ect, nothing obvious, property 13 years old,

I've checked all downstairs and seems to be near the cu as same readings on all, so gonna find out when next their which one the 1st light is, and then test the earth after that to the other lights and I then I'll know more where the issue is.

Would you say this is either a poor connection hidden somewhere or a screw through a cable Ect , any ideas.


What did the IR test results tell you on that particular circuit??
 
I did code it c2 and moved onto rcd side as that was a fix to make it safer for now, and Because I've been asked to go back and Find the problem that's why

Does moving it onto an RCD make it safer? Or does it just leave you liable if any accidents do happen as you carried out work on the circuit last rather than just testing it? Don't forget an RCD only prevents a shock from becoming fatal, not from happening in the first place.
 
I haven't said it's safe, just safer, it took 2 minutes,
And I've noted that it's unsafe so I have made clear, that moving it isn't the solution, it just makes it safer than currently, so until fixed it improved the safety. I'm not liable in my opinion and I feel it was justified.
 
Hum.... not sure I would have bothered moving the circuit onto the RCD side - you may well now have made matters far worse for the client, because instead of just the MCB tripping the RCD might take out more circuits
 
I haven't said it's safe, just safer, it took 2 minutes,
And I've noted that it's unsafe so I have made clear, that moving it isn't the solution, it just makes it safer than currently. I'm not liable in my opinion and I feel it was justified.

Sadly the processes that are put in place after an incident don't consider whether you think you are liable or not.
I'm not having a go here, just trying to help you realise that what you think is helping out may actually be leaving yourself open to a lot of trouble.
Have a read through some of the case stories of prosecutions on the HSE website and you'll see just how easy it is to become liable despite doing what you think is a good thing. I've found it quite scary reading and thinking about some of the things I've done to 'improve a situation' in the short term.
 
Hi all

Done an EICR today and on one light circuit my zs tests was coming with error so got the 2 poor tester out, and I'm getting 50v between 230 l-n and 50v l-e

Checked all switches and light fittings Ect, nothing obvious, property 13 years old,

I've checked all downstairs and seems to be near the cu as same readings on all, so gonna find out when next their which one the 1st light is, and then test the earth after that to the other lights and I then I'll know more where the issue is.

Would you say this is either a poor connection hidden somewhere or a screw through a cable Ect , any ideas.


What ir results did you get and was r1/r2 results at every lighting point satisfactory.? Did you remove cpc ftom earth bar when testing.? And what is earthing arrangement.?
 

Reply to EICR readings in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

A BG fused connection unit, with neon. A boiler. Fuse out. Spur switched off. I was checking polarity after a colleague had 2nd fixed it and...
Replies
7
Views
750
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
728
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
859
Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
1K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock