Discuss EICR report took 3 months to be sent to me... in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Shamus

DIY
Reaction score
0
Hi

I'm looking for some advice please.

I had an electrician do an EICR on my home at the beginning of April 2021. It then took them till July to send the report. In the report they listed several things with a C2 "Potentially dangerous. Urgent remedial action required."

One of the things they listed as a C2 actually went wrong towards the end of June resulting in me having to call out an emergency electrician on a Friday night (not cheap!). If they'd sent me the EICR straight after doing it then I would have carried out the work required and avoided paying for an emergency electrician!

The electrician that did the EICR is now demanding payment. However, they knew that there were potentially dangerous issues in my home but it then took them nearly 3 months to tell me about them! Surely this is a questionable level of service and standards? Am I within my rights to not pay for this EICR?

Thanks

Shamus
 
Last edited:
Pay them the cost of the EICR minus the cost of the emergency call out, explain the thinking in a letter to them.
that's exactly what I was thinking Mike. I just wanted to ask the question here before doing it so I could get some more advice.
Have they broken any electrical standards though? Surely in any line of work that deals with Risk, if you are aware of a risk/hazard but say nothing about it, then you are failing in your duty...?
 
What were their terms and conditions and what was the issue which needed the emergency call out.
 
What were their terms and conditions and what was the issue which needed the emergency call out.
They didn't tell me their terms and conditions, they didn't even tell me there was a charge for the report (in my naivety I assumed I would just pay for all the things that needed correcting).

On the report this is the C2 that caused a problem:
"Outside IP JB Not Glanded Correctly Allowing Water Ingress & No CPC Continuity On Armouring "
 
There should not have been an extra charge for the Report it should have been costed into the overall price. Did they hold you to ransom for a further charge.
 
Don't think they have broken any electrical standards unless the premises are rented, but leaving you uninformed of "Potentially dangerous. Urgent remedial action required." is unprofessional at the very least irrespective of any terms and conditions if any, did you actually see or sign a contract with them? if no then it's your word against theirs to any terms and conditions that you or they wish to apply, in other words you can say anything that you verbally agreed to apply to the terms of work they carried out, and they accepted those terms by performance of the work, equally they can say the same, I would just pay less the amount for the emergency call out and see how it works out from there.
 
There is a big difference between a C2, potentially dangerous and a C1, immediate danger.

The electrician may have judged it a C2, not believing it could get worse in such a short period of time.

Did he mention this to you at the time? Ie, “try not to use that until it’s fixed”

it was water ingress to an outside joint box, you say?
What was it supplying? Did it really need an emergency electrician call out ?

I’m not trying to excuse the lateness in issuing the report, but maybe this particular chap has had a bad turn following COVID? We dont know.
 
There is a big difference between a C2, potentially dangerous and a C1, immediate danger.

The electrician may have judged it a C2, not believing it could get worse in such a short period of time.

Did he mention this to you at the time? Ie, “try not to use that until it’s fixed”

it was water ingress to an outside joint box, you say?
What was it supplying? Did it really need an emergency electrician call out ?

I’m not trying to excuse the lateness in issuing the report, but maybe this particular chap has had a bad turn following COVID? We dont know.
Hello
In my job I have a part time role as a Trade Union H&S rep. I would get into a lot of trouble if I did a risk assessment of a site and then took nearly 3 months to let people know of potential dangers...

They didn't mention anything at the time. As they left they said they'd get in touch soon with prices to sort the issues out.

Regarding the emergency call out. When the electrics went out they went out for the whole property. It was the emergency electrician who came out and identified where the problem was.

Yes, the company blamed the lateness of the report on covid and being really busy...
 
One thing is not clear, what prompted the electrician to carry out an EICR in the first instance?
we live in an old house and were waiting to have work start on an extension. we were told to make sure our fuse board was suitable before the work started and the company said they would need to do an EICR as well
 
What company said they would need to do an EICR as well, the Builder or the electrician who is going to be putting in the electrics for the extension? Also who told you to ensure your existing fuse board was suitable?
 
Was that in the terms and conditions that you signed at the beginning of the contract, and don't forget to add on an administration fee and costs for the three months you have been waiting for the EICR where you incurred additional cost for the bridging loan you took out to cover the costs of the extension which has been unable to be started because of the lack of certification.
 
something else I have just noted. The EICR has been signed off (inspector and Tester) by the owner of the company, NOT the actual electricians who came out. Is that allowed...?
Section 9 on the EICR should make that clear, the words I/We should be crossed through as appropriate.
 
Regarding the emergency call out. When the electrics went out they went out for the whole property. It was the emergency electrician who came out and identified where the problem was.
Are you saying that water ingress to an external box caused a power loss to the whole property????

I'm thinking the only 'box' susceptible in such a situation would belong to the supply authority.

RCD main switch or something?

More information is needed. All sorts of thoughts.
 
Why disagree @Risteard, any incorrect or incomplete clause or reference in an EICR would constitute an incorrectly filed out form, look at this from the consumer/customer side not that of the electrician.
 
Why disagree @Risteard, any incorrect or incomplete clause or reference in an EICR would constitute an incorrectly filed out form, look at this from the consumer/customer side not that of the electrician.
I/We not being crossed out is tenuous at best. In fact most software won't give you the option. In fact the foreslash essentially means "or", so it's not grammatically incorrect for it not to be crossed out. It would be wholly unreasonable grounds for withholding payment.
 
IMO if the software will not allow the option to be used then the software is defective, if the I/We option is not important why is it there, it's the same as not completing any line in the report.
 
IMO if the software will not allow the option to be used then the software is defective, if the I/We option is not important why is it there, it's the same as not completing any line in the report.
Where an either/or option exists on the model forms (for example kVA/amps, or SATISFACTORY/UNSATISFACTORY), it is followed with 'delete as appropriate'.

I/we isn't intended as such an option, as it isn't followed by 'delete as appropriate'. As @Risteard points out, totally unreasonable to withhold payment for that reason.
 
Why disagree @Risteard, any incorrect or incomplete clause or reference in an EICR would constitute an incorrectly filed out form, look at this from the consumer/customer side not that of the electrician.
Really worried now……honestly!
Hundreds of our Certs from the last twenty years incorrectly completed?
NICEIC at fault too, for allowing a member to desecrate their certificates, are they?
Agree with the disagree.
 
Last edited:
Why disagree @Risteard, any incorrect or incomplete clause or reference in an EICR would constitute an incorrectly filed out form, look at this from the consumer/customer side not that of the electrician.
Blimey Mike.
It took you almost a year to ask why risteard disagreed! 😂
I wonder how it all ended for @Shamus
 
I feel cheated when there isn't a proper ending to a thread. I.e knowing the outcome. So I shall embellish as I doubt we'll ever see shamus again..
Shamus decided to make a part payment towards the EICR. He withheld a small portion towards the cost of the remedial work. He explained why he had done this in a politely, yet assertively written email to the company in question.
They fully understood and applauded his reasoning. They all lived happily ever after.

Phew, I can relax now.
 
Blimey Mike.
It took you almost a year to ask why risteard disagreed! 😂
I wonder how it all ended for @Shamus
In his defence I linked to this thread from another thread so the "disagree" was recent as opposed to dating back to when the thread was at its prime. I stand by "I/We" not being intended to be crossed out though. As pointed out by @Pretty Mouth there is no instruction to "delete as appropriate" for it.
 
In his defence I linked to this thread from another thread so the "disagree" was recent as opposed to dating back to when the thread was at its prime. I stand by "I/We" not being intended to be crossed out though. As pointed out by @Pretty Mouth there is no instruction to "delete as appropriate" for it.
Thought the 'X' might have been recent.....made sense.
 

Reply to EICR report took 3 months to be sent to me... in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I've recently has an EICR (report attached) carried out on my two bed flat because I need to rent it out for a year. The electrician has come back...
Replies
19
Views
984
Hi all, we are purchasing our first home and the sellers had an EICR carried out in April 2023. They have sent us a copy of the report and said...
Replies
3
Views
891
So I've recently had an EICR for my building. Came back with about 20 odd C2 remedials and a few F1's which resulted in UNSATISFACTORY being...
Replies
5
Views
1K
I paid an electrician for an EICR test - two of his men took 3-4hrs to do the test. This was on 28/04. He since told me that the test failed and...
Replies
11
Views
2K
I commissioned an EICR to be done on a property that is in Wales as this is now a requirement in order to let on any new tenancies after 1st...
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock