Discuss EICR Test Fail, before and after in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi, recently had an EICR test done by 'Landlord Certificates' which failed due to circuite 3 having two radial circuits into a single 32amp MCB, they advised splitting it into two 20amp MCB's and quoted £174 including EICR certificate. The Electrian appears to have simply taken out the 32amp MCB's and put in a 20amp and 16amp. Was the original actually a fail? And is what the Electrician has done now acceptable?
Before and After.JPG
 
I imagine the 32a 'radial' (2 cables in the MCB) actually used to be a Ring and has now been infected / broken and lost its Ring continuity.
The correct cause of action would be first to try and correct the break and reinstate the original Ring.
If that is not possible then both cables could be put into one 20amp MCB,

If they are in fact 2 completely separate radials ( with no cross connections ) then they can be put on 2 separate MCBs , 16 amp or 20amp is fine
 
do you have any previous reports for the electrical installation?
 
the installation cert for the consumer unit change would be a really useful thing to dig out and post here.
in particular the page marked "schedule of circuits"
 
I imagine the 32a 'radial' (2 cables in the MCB) actually used to be a Ring and has now been infected / broken and lost its Ring continuity.
The correct cause of action would be first to try and correct the break and reinstate the original Ring.
If that is not possible then both cables could be put into one 20amp MCB,

If they are in fact 2 completely separate radials ( with no cross connections ) then they can be put on 2 separate MCBs , 16 amp or 20amp is fine
Thanks, it is an old building, probably had loads of messing around with the electrics over the years, so makes sense a ring may have become broken, I wonder why the guy who fitted the fuse box couldn't have come to the same conclusion as the EICR tester.
 
Thanks, it is an old building, probably had loads of messing around with the electrics over the years, so makes sense a ring may have become broken, I wonder why the guy who fitted the fuse box couldn't have come to the same conclusion as the EICR tester.
The sparks who changed the board might not have done end to end tests on the ring and just assumed it is a ring.
Without the original install cert with test results we will never know what was tested.
I am guess the guy doing the EICR has done end to end and can't get continuity of Ring
 
I take it they didn't comment on some awful connections in the consumer unit and the missing busbar shield.
They did, I had a new boiler installed recently and the guy who wired in the thermostat also commented on how intidy it is, bit dissapointing given what it cost but what can I do? Some people have no pride in their work, but it is safe I assume, especially with the EICR just done.
 

Reply to EICR Test Fail, before and after in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I had an eicr done in 2021and it passed with four C3 items. They recommend next test date to be in 3 years instead of 5 on the certificate...
Replies
15
Views
1K
Good morning, We have a two-bedroom flat that my wife and I rent out to supplement our income. Following the recent EICR, several issues...
Replies
42
Views
2K
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
868
I paid an electrician for an EICR test - two of his men took 3-4hrs to do the test. This was on 28/04. He since told me that the test failed and...
Replies
11
Views
2K
For example the house today had two lighting T&E in the same MCB. I know it's fine, but as I test both 'radials' where and how do we enter them on...
Replies
6
Views
856

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock