Discuss EICR tick sheet other methods of protection in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

It is very tenuous and unclear as I don't deem any part of the insulation or sheath as reinforced. The Reg considers the insulation, not the sheath as I read it is at least the equivalent to the requirements of reinforced insulation. I actually find that difficult to believe.

The Ref is referencing cables that are DI not RI.
 
Thanks for all the responses. I've always believed the section on other methods of protection was referring to the installation as a whole and not just an individual circuit or circuits. I've read through the relevent sections in the regs book but the wording of it isn't always the easiest thing to get your head round
 
I tend to consider that it would only be applicable for a situation where that method of protection is the sole means of providing basic and fault protection. Because ADS is so prevalent this is likely to be in place and so the other method will not be the sole means and so ADS will apply.
 
As far as I am aware, this tick box has only been for EICs since the 17th 1st amendment?
It has been slightly altered for the 18th, in an attempt to clarify this particular issue.

Anyway, to answer the OP, yes other methods of protection should be ticked, if they are in use.

Meter tails have reinforced insulation, which satisfies the requirements for double insulation.
T&E does not, as the live conductors only have a single layer of insulation between them and the CPC.
 

Reply to EICR tick sheet other methods of protection in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I've recently has an EICR (report attached) carried out on my two bed flat because I need to rent it out for a year. The electrician has come back...
Replies
19
Views
914
I am a landlord and my managing estate agent just recently organised an electrician to carry out EICR. Came back as unsatisfactory, no RCD...
Replies
27
Views
7K
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
854
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
737
I commissioned an EICR to be done on a property that is in Wales as this is now a requirement in order to let on any new tenancies after 1st...
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock