Discuss Eicr in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Charlie_

-
Esteemed
Arms
Reaction score
1,845
Large commercial office
Installation circa 1996.

Asked to price up some work further to a PI being carried out.

I called in yesterday for a quick chat.
The EICR has multiple C1, 2 and 3 recorded but still satisfactory overall.

They have a 9.8 @ 240 (9.0 @ 230) shower in a ladies toilet wired in 6mm singles and protected by a 40a MCB that was given a C1 due to cables being melted at MCB terminal.
Live snipped and left floating.
Their Recommendation; rewire circuit with 10mm and change MCB to RCBO. 10m run

The single phase mc board supplying the circuit also had 4 SWAs glanded and bolted to its base.
There was no tags from the bolts to the earth bar.. Coded C2.

No RCD protection for sockets throughout building.. C1
Missing consumer blanks.. C2. Still missing.

I am going back next week to go through the report, should be interesting.
 
Large commercial office
Installation circa 1996.

Asked to price up some work further to a PI being carried out.

I called in yesterday for a quick chat.
The EICR has multiple C1, 2 and 3 recorded but still satisfactory overall.

They have a 9.8 @ 240 (9.0 @ 230) shower in a ladies toilet wired in 6mm singles and protected by a 40a MCB that was given a C1 due to cables being melted at MCB terminal.
Live snipped and left floating.
Their Recommendation; rewire circuit with 10mm and change MCB to RCBO. 10m run

The single phase mc board supplying the circuit also had 4 SWAs glanded and bolted to its base.
There was no tags from the bolts to the earth bar.. Coded C2.

No RCD protection for sockets throughout building.. C1
Missing consumer blanks.. C2. Still missing.

I am going back next week to go through the report, should be interesting.

Which renders the EICR worthless.

C1 and satisfactory - no.
 
Large commercial office
Installation circa 1996.

Asked to price up some work further to a PI being carried out.

I called in yesterday for a quick chat.
The EICR has multiple C1, 2 and 3 recorded but still satisfactory overall.

They have a 9.8 @ 240 (9.0 @ 230) shower in a ladies toilet wired in 6mm singles and protected by a 40a MCB that was given a C1 due to cables being melted at MCB terminal.
Live snipped and left floating.
Their Recommendation; rewire circuit with 10mm and change MCB to RCBO. 10m run

The single phase mc board supplying the circuit also had 4 SWAs glanded and bolted to its base.
There was no tags from the bolts to the earth bar.. Coded C2.

No RCD protection for sockets throughout building.. C1
Missing consumer blanks.. C2. Still missing.

I am going back next week to go through the report, should be interesting.

Write a letter to facilitate the recipient of the EICR getting a refund. Refer to the passages in the regs and GN3 that render this report useless and the person who carried it out incompetent. The coding errors can be tackled by reference to the ESC EICR guide. Encourage the client to complain to the scheme if they get no luck with the contractor, and offer your help in doing so.
These clowns need to learn that they cannot get away with it. It's incompetent at best, and at worst fraudulent.
 
Write a letter to facilitate the recipient of the EICR getting a refund. Refer to the passages in the regs and GN3 that render this report useless and the person who carried it out incompetent. The coding errors can be tackled by reference to the ESC EICR guide. Encourage the client to complain to the scheme if they get no luck with the contractor, and offer your help in doing so.
These clowns need to learn that they cannot get away with it. It's incompetent at best, and at worst fraudulent.

I think that's the way its probably going to end up going.
Was only there for a short while on Friday so we only had a brief chat.
The other company have submitted the EICR along with quotes for many remedial works.
I'm shooting myself in the foot as I will be doing myself out of remedial works..

This type of thing seems to becoming more common, you are right they can't get away with it, whether it's due to incompetence or crookedness.
 
If they were touting for the remedials why would they put "satisfactory"??

Surely they would correctly put "unsatisfactory"

I haven't got a clue but come next week they will need to be explaining what's gone on.
going back next week to scrutinize the EICR and determine what remedial work actually needs doing.
I'm thinking it's more likely down to incompetence but then more senior members of the company have compiled the report and then submitted the quotes
 
Last edited:
Absolute joke... Overall satisfactory with C1 & C2 departures recorded and to top it the observation codes attributed to the departures highlighted are incorrect. Just shows you how dangerous a little knowledge really is!! Hope his indemnity insurance is active...he may need it!!
 
Since when has a socket lacking RCD protection ever been a C1???!!! Immediate action required[emoji23][emoji23][emoji23] Whereas the missing fuseboard blanks probably leaving exposed terminals accessible with tools and fingers only gets a C2 and he decides to leave it as is. Our industry is becoming a laughing stock by idiots like that[emoji35][emoji35][emoji35]
 
Since when has a socket lacking RCD protection ever been a C1???!!! Immediate action required[emoji23][emoji23][emoji23] Whereas the missing fuseboard blanks probably leaving exposed terminals accessible with tools and fingers only gets a C2 and he decides to leave it as is. Our industry is becoming a laughing stock by idiots like that[emoji35][emoji35][emoji35]
even with blanks fitted some DBs could fall into c1 as blanks can be removed without tool
 
Thats my point entirely it warrants a C1 and sorting straight away yet matey boy gives it a C2 and walks away from it as is.... then charges for the privilege of the report he's cobbled together. [emoji35][emoji35]
 

Reply to Eicr in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

My wife is on the committee of the local village, and they have just had an EICR carried out. This came out as 'unsatisfactory' and accompanied by...
Replies
14
Views
3K
Evening all. I did an EICR recently and then changed a consumer unit. As part of the EICR process I take off around 25% of all accessories to...
Replies
9
Views
2K
Hi, I don't tend to do EICR's that often, and have just done one and wanted a little advice as to if my codings are correct or maybe little over...
Replies
25
Views
9K
Hi, been to job today to install a new bathroom light & fan in a HMO. The 1st & 2nd floors are fed via a second db on the first floor - db2...
Replies
31
Views
5K
E
I think I've Posted this before, but I've just updated it. Some of the sparks where I work still get a little confused of what the different areas...
Replies
58
Views
77K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock