Discuss Electric Radiators on an RFC in the UK Electrical Forum area at ElectriciansForums.net

Midwest

-
Esteemed
Arms
Reaction score
10,616
Here's one for a Sunday. I need some advice please.

I went to quote for a job yesterday, where my client is replacing the aged electric convector panel heaters in her flat with some new electric radiators.

I was asked to remove one of the old ones. All the existing heaters are connected to FCU's. Having done a visual inspection of the supply circuit, I noted it was in fact a dedicated 32A RFC (i.e. only used for the heaters), wired in 2.5mm tw&e, as opposed a 32A radial.

The current load is 3750w, made up of 3 x 1000w & 1 x 750w (16.3A @ 230v). The new load would be 4750w, made up of 1 x 2000w, 2 x 1000w & 1 x 750w (20.6A @ 230v). These new heaters have been chosen by the manufacturers, by the dimensions of each room etc.

I understand appendix 15 gives guidance on not supplying electric space heating on RFC's, and reg 433.1.204 (on RFC's) 'if the current carrying capacity of the cable is not less than 20A... etc'.

The reference method would I guess be A, giving a ccc of 20A for 2.5mm.

Your thoughts?
 
Hi MW - I'm thinking the heaters are likely spaced out around the ring in different rooms and so RFC point load is not a concern(?). And with a total load of just over 20A using a dedicated 32A RFC for them seems ok to me.
 
At mine I've just changed out a wall rad from 1.5kW to 3kW in the kitchen, it's on a manufacturer's plug as was its predecessor. And its plugged into the only kitchen RFC I've got, along with the toaster, kettle, fridge, washer, dryer, dishwasher, boiler and every other thing it seems. I do (finally) feel guilty enough to break out the tools and put in a new circuit for it. But I've been told to wait till wifey is away ...
 
Sounds fine to me. A fixed load of about 20A on a circuit correctly rated at 32A. No chance of any additional load being plugged in.

My view on the ring final circuit notes in Appendix 15 is that they relate to a general power circuit with socket outlets and FCUs, not a dedicated heating circuit.
 

Reply to Electric Radiators on an RFC in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm interested in a house built around the 1980's in Northern Ireland. I took a few photos of the consumer unit etc. which is situated in the...
Replies
0
Views
741
Hi all looking for a bit of advice. I've been asked to price a rewire for a early 70's build 2 bed apartment. The apartment block was built in the...
Replies
1
Views
3K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock