Currently reading:
electric shower tripping

Discuss electric shower tripping in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
15
Been asked to find out why a new shower is tripping a new cu rcd,
new shower 9.8kw mira
supplied with 10mm T&E
40amp mcb protected by 63a RCD
Its a new cable thats been run in and I have no equipment to test the continuity etc I went right back to basics ,missed out the 45amp DP switch and it still tripped,then wired it straight into the DP isolator switch of the cu and the shower started straight away I should also say that this cu is fed from the main house but the shower did not trip the main cu.
The mira instructions say to fit a 30a rcd

Anyone any ideas ?

Ta
 
Wonder if the OP is charging for this?

So its a recent install, the customer bought the kit, the installer isn't returning calls, the OCPD may be too low, we don't know if the RCD or MCB are tripping.

We do know the person fault finding doesn't have the appropriate kit.

Has it ever worked?

Did the installer provide a cert?

Wonderful!
1.no, i have a pension i dont need to charge
2.ok i should have taken notice of this
3.ministry of bleeding obvious....new install tripping...course its never worked
4.of course not he's disappeared with his money
As a long time ex sparky i enjoy reading most of these threads to try and keep up but some of you guys and your replys just fill me with dismay with the sarkiness and all round General contempt you treat genuine querys. unless i
 
@neilyboy: In your original post you said that you were looking for a fault on a 9.8 kW shower, that was fed via a 40a MCB & 63a rcd which trips when the shower is turned on.
You have no test equipment & decided to fault find by first bypassing the switch, then connecting the shower to the incoming mains supply. Neither of which are safe or recognised fault finding techniques, then come here & ask for help.
You were given the most probable causes by telectrix & others in the first few replies you got. The people who've taken the time to reply to you, do this job day in / out & get annoyed when people use dangerous practices to try to find a fault. So yes you will get sarcastic & contemptuous replies.
My best suggestion to you now would be to tell your friend to contact a proper electrician in, who has the correct knowledge & equipment to find and clear the fault safely.
 
Last edited by a moderator:
Funny I get 43a

Then presumably you've calculate s it using the wrong voltage. The power rating system of appliances are still given at 240V almost universally, many will have their 230V power rating given additionally in smaller writing.

A resistive load of 9.8kW at 240V will only be around 9kW at 230V
 
From a design perspective @davesparks , while I appreciate technically you are correct, using 230v as the nominal voltage in calculations gives you a safer margin of error in cable selection. This is also specified at pg 316 BS7671. Now before you say well if you do that by the time you get to 30v you would end up with 9800/say, 30v = 326 amps...Design parameters dont go down from 230v. So who of you calculate say PFC with anything but 230xCmin/Zs or ccc with anything but xw/230? And I do understand if you take the resistance of the element and R =V/I and manufacturers instructions and specifications, but still if I was designing the circuit and deciding on the cable that is the way I have been taught. And I have had this "discussion" before and taken it back and written the various viewpoints calculations up on the whiteboard from both viewpoints and the tutor in question still insisted that all design calculations assume harmonised voltage, which at the end of the day only makes things safer. Let fly the dogs of war!
 
Last edited by a moderator:
From a design perspective @davesparks , while I appreciate technically you are correct, using 230v as the nominal voltage in calculations gives you a safer margin of error in cable selection. This is also specified at pg 316 BS7671. Now before you say well if you do that by the time you get to 30v you would end up with 9800/say, 30v = 326 amps...Design parameters dont go down from 230v. So who of you calculate say PFC with anything but 230xCmin/Zs or ccc with anything but xw/230? And I do understand if you take the resistance of the element and R =V/I and manufacturers instructions and specifications, but still if I was designing the circuit and deciding on the cable that is the way I have been taught. And I have had this "discussion" before and taken it back and written the various viewpoints calculations from both viewpoints and the tutor in question still insisted that all design calculations assume harmonised voltage, which at the end of the day only makes things safer. Let fly the dogs of war!

I'm sure that it's easier just to say 'up yours' - but since you went to all the trouble, good post @Vortigern
 
Yes i am real
And what holes ,why do you feel the need to put friend in inverted commas

Hum..

What holes - clear admission of insufficient test kit, random approach to testing, didn't confirm in initial post it had never worked

"friend" - If I had £1 for everybody that initially claimed to be doing this for a friend on here I could probably have a decent holiday...

Just saying.
 
take a load of 10kW @ 240V for example.

P=I V so I = P/V = 10,000/240 = 41.667A

from that using ohm's law, R = V/I = 5.76 ohms

now assume that V =230V

I =V/R, so I= 230/5.76 = 39.93A

so @ 230V P = VI = 9.184kW.
This is what Pete999 or was it telectrix posted in support of the previous "discussion" re counter argument to using 230v which is undeniable. I just post this to save you having to re-post it. I get it.
 
From a design perspective @davesparks , while I appreciate technically you are correct, using 230v as the nominal voltage in calculations gives you a safer margin of error in cable selection. This is also specified at pg 316 BS7671. Now before you say well if you do that by the time you get to 30v you would end up with 9800/say, 30v = 326 amps...Design parameters dont go down from 230v. So who of you calculate say PFC with anything but 230xCmin/Zs or ccc with anything but xw/230? And I do understand if you take the resistance of the element and R =V/I and manufacturers instructions and specifications, but still if I was designing the circuit and deciding on the cable that is the way I have been taught. And I have had this "discussion" before and taken it back and written the various viewpoints calculations up on the whiteboard from both viewpoints and the tutor in question still insisted that all design calculations assume harmonised voltage, which at the end of the day only makes things safer. Let fly the dogs of war!

There is no need to add artificial margins of error in to these calculations, the cable ratings we use have quite enough margin and headroom built in to them already.

If you have a piece of equipment where the data plate quotes power rating A at 240V and power rating B at 230V then it is just plain wrong to calculate based on rating A at 230V.
You can't say that design parameters don't go down below 230 therefore we can happily ignore the facts.
The calculations for Zs that you mention are not relevant to this point, they have to be based on the nominal value because the mains voltage is not fixed at a specific value, the power ratings of an appliance are fixed at a specific value at a specific voltage.

The opinion of one tutor is not going to change pure scientific fact.

I just don't understand how people can be so blind to the laws of physics
 
Well as I said I can agree with your viewpoint without slur or demur, however there is it seems another viewpoint that does ignore your science and goes for a margin that obviously you dis-agree with. If you are truly based on scientific fact you will of course be aware that very often we get (or at least I do) 247/9 v. What do you do with that scientifically measured fact in design? And what if in the future tappings are changed to 230v? Do you inbuild future possibilities like someone adding a couple of sockets and a cooker to a ring for instance? Please bear in mind I am acting devils advocate as this subject bugs me and it is meant in a spirit of enquiry and healthy discussion.
 
Last edited by a moderator:
I dont have a megger, I have a fluke, Installation practices of 40 odd years ago are still practiced today,its the way they are installed ie bad workmanship that cause the problems,wiring systems have not changed since I was on the tools but certain regs have,earthing,testing,circuit discrimination I could go on but ultimately most of it is down to bad practice.
I would have had my a**e booted from my journeyman for some of the installations I have seen
Bad workmanship has not changed it existed 40 years ago as it does today but installation practices have changed considerably. Now there are much refined methods of fault tracing brought into being because the old ways were not sufficiently reliable. To attempt such work now it is advisable to first become fully aware of all the parameters involved. I trained in the early 60s but would in no way say that the "things" are still the same things, the basic circuit principle is but the method of safe control has been much enhanced. We no longer look round for a metal water pipe to wrap an earth wire around.
 
Well as I said I can agree with your viewpoint without slur or demur, however there is it seems another viewpoint that does ignore your science and goes for a margin that obviously you dis-agree with. If you are truly based on scientific fact you will of course be aware that very often we get (or at least I do) 247/9 v. What do you do with that scientifically measured fact in design? And what if in the future tappings are changed to 230v? Do you inbuild future possibilities like someone adding a couple of sockets and a cooker to a ring for instance? Please bear in mind I am acting devils advocate as this subject bugs me and it is meant in a spirit of enquiry and healthy discussion.

It's not my science, it doesn't belong to me, it's just the laws of physics. You might as well be disagreeing with gravity. I disagree with adding an extra margin on top of the margins that have already been allowed in the system, it just leads to a waste of materials. It's not just in electrics that I have this debate, it's in other areas I work too.

I am aware of the fact that substations in the U.K. Output at 250V/433V, even the brand new ones being built today are the same. they don't normally have any option to change this at that level, the tap changers are normally only fitted at the 11kV level, so to actually drop to 230V they would have to lower the 11kV network. There are many problem with doing this so I think it is fairly safe to say that it isn't going to be happening any time soon.

The ring circuit is by its nature already designed with the ability to have additional sockets added, but is again irrelevant to the question.

You seem to be confusing the original point, which is that a fixed load rated at 240V you should calculate at 240V, with other areas where you don't have fixed values to work with and consequently would use the nominal value.

There are many areas in design guides, BS7671 and the various guidance notes where we are told that in the absence of better information we should use the nominal values.
 

Reply to electric shower tripping in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock