emergency lights not coming on when breaker is switched off, are these wired just for use as normal lights rather than emergency??? Sorry not done much emergency lights before

AFCAC741-D30C-467D-AF14-1FCA248CBB91.jpeg


D323798B-1783-45F9-A656-4DD969CD38DF.jpeg
 
The lamp holder's not even connected to the battery pack.
 
the wiring looks correct to me,
I presume its a 2D style led panel that is attached. the 4 coloured singles go direct to the led's as a low voltage supply when the mains fails.
have you checked that you get power between N and L1 (next to the earth) at all times and that the power drops out when the breaker is off?
 
the wiring looks correct to me,
I presume its a 2D style led panel that is attached. the 4 coloured singles go direct to the led's as a low voltage supply when the mains fails.
have you checked that you get power between N and L1 (next to the earth) at all times and that the power drops out when the breaker is off?
Yes turn breaker off and no power there
 
it looks like a combined battery and charger unit, I suspect the battery has failed, if its being powered up correctly I would expect a tell tale led to show on the surface of the lamp somewhere (possibly a green led)
when you remove the power, the tell tale lamp should go off and the light normally comes on at half brightness until the battery is flat.

Edit, just zoomed in on picture, confirming the detail above.
 
Last edited:
Does the indicator light work to show the battery is charging?
Just make sure that the internal battery is properly connected in the emergency pack as they can be a bit finicky
 
it looks like a combined battery and charger unit, I suspect the battery has failed, if its being powered up correctly I would expect a tell tale led to show on the surface of the lamp somewhere (possibly a green led)
when you remove the power, the tell tale lamp should go off and the light normally comes on at half brightness until the battery is flat.

Edit, just zoomed in on picture, confirming the detail above.
Yes once power is on the green light comes on, which I presume means it’s charging
 
Did the green charge indicator ever come on, if not the no power to PL. Is the test switch in test mode?

most I've fitted come with some charge in the battery but if these are totally dead then they may require some charging to function.
 
Did the green charge indicator ever come on, if not the no power to PL. Is the test switch in test mode?

most I've fitted come with some charge in the battery but if these are totally dead then they may require some charging to function.
So at the min the lights are switched by photocell and come on at night so the batteries should be charged and test mode does nothing
 
Fed via photocell too

The supply to the battery pack should be from the PL. When the test switch is in the test position then power is cut fooling the light into thinking a loss of power has occurred and the light should switch to battery back up. When not in the test position the batteries will charge indicated by, usually, a green led being lit.

The supply to the lamp, via the contactor and photo cell should be is the switched live and should go in the appropriate terminals on the light.
 
The supply to the battery pack should be from the PL. When the test switch is in the test position then power is cut fooling the light into thinking a loss of power has occurred and the light should switch to battery back up. When not in the test position the batteries will charge indicated by, usually, a green led being lit.

The supply to the lamp, via the contactor and photo cell should be is the switched live and should go in the appropriate terminals on the light.
Thanks understand a bit more now, I’m back tomorrow so will check the wiring cheers for your help
 
Go back to basics initially and check your incoming supply as per #22 it wouldn't be the first time a contactor ditches the PL, if the charge indication goes off when the contactor is off it is connected incorrectly but not necessarily at the fitting. If all this is okay you can probably assume the fitting/s are duff.
 
Right this is what they have now, I’ll do a drawing of what I think it should be and you guys can correct me if I’m wrong? Or any other solutions? Or if anyway has a drawing would be must appreciated haven’t really touched key switches I know it’s a normal switch basically or contactors

2AAC450A-6321-42C7-9315-1F8F86A0763A.jpeg
 
I would be happy to post a wiring diagram, would this fall foul of no step by step instructions rule?
 
Strima


The switched live side feeds direct to the led geartray 230v via the pins and the emergency/perm side go through the module witch should have a built in battery witch would power a second set of led,s on the geartray via the battery in the event of a power outage
 
IMG_0960a.jpg


There are multiple ways of doing it, depending on exactly what function you want from the manual on / off switch and the photocell override switch.
but this is one way it could be achieved.
 
Strima


The switched live side feeds direct to the led geartray 230v via the pins and the emergency/perm side go through the module witch should have a built in battery witch would power a second set of led,s on the geartray via the battery in the event of a power outage
That just seems like a lot of faff...

To be fair all the 2D EM fittings I've dealt with were solely 2D with no additional LED lamps hence my comment.
 
That looks wrong to me, the p/c override and supply for the control.

depends on what you are trying to achieve.
if you want the lights
perm on, turn manual switch to on.
automatic, turn manual switch to off with over ride switch on
perm off, turn manual switch to off and over ride switch to off
 

Reply to Emergency lights or standard in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
671
Hi Guys I've fitted a few emergency lighting circuits to both domestic and commercial installs before, I've come across one I can't get my head...
Replies
19
Views
1K
Hi folks, Can anyone recommend a reliable brand for emergency lighting bulkheads please? I have a job coming up to replace 30 odd units. I have...
Replies
2
Views
509
Morning Needing help regarding Ansell AARDRINA/DD1/SM3. I’ve installed 6 in one room, one being an emergency light fitting. All 5 standard...
Replies
15
Views
542
Hi guys, Been asked to fit 2 lights and a switch, which in reality turned out to be rewiring a multiple PIR setup to a single switch, adding...
Replies
0
Views
901

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock