- Reaction score
- 51
emergency lights not coming on when breaker is switched off, are these wired just for use as normal lights rather than emergency??? Sorry not done much emergency lights before
Discuss Emergency lights or standard in the UK Electrical Forum area at ElectriciansForums.net
Overthinking, will linking 1 and 2 work with emergencyThe lamp holder's not even connected to the battery pack.
Yes turn breaker off and no power therethe wiring looks correct to me,
I presume its a 2D style led panel that is attached. the 4 coloured singles go direct to the led's as a low voltage supply when the mains fails.
have you checked that you get power between N and L1 (next to the earth) at all times and that the power drops out when the breaker is off?
YesHave you actually connected the battery.
Yes once power is on the green light comes on, which I presume means it’s chargingit looks like a combined battery and charger unit, I suspect the battery has failed, if its being powered up correctly I would expect a tell tale led to show on the surface of the lamp somewhere (possibly a green led)
when you remove the power, the tell tale lamp should go off and the light normally comes on at half brightness until the battery is flat.
Edit, just zoomed in on picture, confirming the detail above.
Ok will check but did check 2 lights and they was the same no light once breaker was offDoes the indicator light work to show the battery is charging?
Just make sure that the internal battery is properly connected in the emergency pack as they can be a bit finicky
Outside toilet block, all inside emergencies workthe battery is not connected or the battery has failed, what environment is this fitting installed in?
Perm is from breaker to contactor then lightsAre the switch and perm lives fed from the same breaker?
Surely that's arse about face, PL should be from test switch and SL from contractor?Perm is from breaker to contactor then lights
Switch is straight from key switch but nothing happens when switching key switch
So at the min the lights are switched by photocell and come on at night so the batteries should be charged and test mode does nothingDid the green charge indicator ever come on, if not the no power to PL. Is the test switch in test mode?
most I've fitted come with some charge in the battery but if these are totally dead then they may require some charging to function.
Fed via photocell tooSurely that's arse about face, PL should be from test switch and SL from contractor?
Fed via photocell too
Thanks understand a bit more now, I’m back tomorrow so will check the wiring cheers for your helpThe supply to the battery pack should be from the PL. When the test switch is in the test position then power is cut fooling the light into thinking a loss of power has occurred and the light should switch to battery back up. When not in the test position the batteries will charge indicated by, usually, a green led being lit.
The supply to the lamp, via the contactor and photo cell should be is the switched live and should go in the appropriate terminals on the light.
Please tell me you are not still at that caravan site
You have a good memory and no I’m not hahaPlease tell me you are not still at that caravan site
It was yes hahaIs that the one with the two phases and all that jazz?
Good thanks, it was split phase supply had SSE come out to test aswell as they had one of there consultants check before we even went to say it was 3 phase but it wasn’t must have forgot his testers hahaHow did that job go?
Everything work out ok for you?
No crack on Bradley is a sparky. It's the DIYers we tend to not give step by step advice.I would be happy to post a wiring diagram, would this fall foul of no step by step instructions rule?
It’s the contactor bit how do you incorporate thatTo keep it simple think of the test/key switch as the main on/off for the circuit.
RCBO to key switch-leg 1
I’ll have a go won’t be long hahaNo crack on Bradley is a sparky. It's the DIYers we tend to not give step by step advice.
That just seems like a lot of faff...Strima
The switched live side feeds direct to the led geartray 230v via the pins and the emergency/perm side go through the module witch should have a built in battery witch would power a second set of led,s on the geartray via the battery in the event of a power outage
That looks wrong to me, the p/c override and supply for the control.
It’s the contactor bit how do you incorporate that
Cheers mate, what software you use to draw thatHere’s more detailed schematics, if it’s any help.
View attachment 49647
Well I ain't posting mine now, hour of my life I'm not getting back.Here’s more detailed schematics, if it’s any help.
View attachment 49647
Noooo I appreciate your helpWell I ain't posting mine now, hour of my life I'm not getting back.
Reply to Emergency lights or standard in the UK Electrical Forum area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.