Taken from www.firemagazine.com



Crown Court sentence for fire alarm engineer

A former retained firefighter from Wales who failed to maintain a fire alarm in a care home will face sentence next week after being the first fire alarm engineer to be prosecuted as a responsible person under the Regulatory Reform (Fire Safety) Order 2005.
Trafford Magistrates Court heard Christopher Morris, 56, of Llandudno, North Wales, plead guilty to two charges of failing to maintain a fire alarm system at a care home in Trafford, Manchester, to a recognised standard and failing to inform the owners of the home of the deficiencies in the system.
Morris will be sentenced at Manchester Crown Court on December 23, after the bench decided it did not have sufficient powers to deal with the case and what they described as ‘culpable neglect’ by the defendant.
The case was brought to court by Greater Manchester Fire and Rescue Authority in what is believed to be the first of its kind under the Regulatory Reform (Fire Safety) Order 2005. The law allows the fire and rescue authority to prosecute a person who has responsibility for a particular area of premises or, as in this case, maintaining fire equipment that requires specialist knowledge or skills to carry out repairs.
Deputy County Fire Officer Jim Owen said it would send a strong message throughout the fire industry that fire and rescue authorities in England and Wales will not hesitate in taking firm action against anyone that falls short of their obligations under fire legislation.
Mr Owen said: “Whilst many owners have been prosecuted under the Fire Safety Order, this may be the first time a fire and rescue authority has prosecuted someone contracted by the owner of a property to maintain a fire alarm. Taking on such a contract extends the requirements of the order to the fire alarm engineer. Anyone we find who doesn’t carry out their work to recognised standards is a danger and we won’t hesitate to take action.”
The court heard how Greater Manchester Fire and Rescue Service attended a fire incident at a care home in Trafford in May 2009 in which an elderly woman died. During subsequent investigations into the fire safety arrangements at the premises, fire safety enforcement officers commissioned an examination of the fire alarm system by a specialist consultant who sits on the British Standard committee for fire alarm systems.
The examination report revealed that the system was estimated to have been installed during the late 1980s or early 1990s and that a number of issues were discovered within the panel that demonstrated poor practice remedial work had been carried out at some time during its lifetime. This included:
  • A blown fuse over-ridden with a piece of wire
  • An electronic component had been suspended between two terminal bocks instead of being attached to the circuit board
  • An alarm silence/fault warning buzzer was missing from the circuit board
  • The fault warning light on the front face of the panel had been almost covered by paint.
Christopher Morris, an electrician who had taken over the maintenance of the system in 2006, had issued several annual certificates of worthiness to the owner of the home, stating the system was 100 per cent.

During an interview under caution, Morris initially claimed that although the system was old it was compliant with the relevant British Standard. However, when he was challenged about the poor repair issues and shown the specialists photographs he admitted that he was not aware of them.
Morris will appear at Manchester Crown Court for sentencing on Thursday, December 23, 2010.
 
Enough said.

To be fair, that's an extreme example of laziness, but it happens, and isn't the half of what we've seen out there.

It does highlight the need for skill and proper attention, especially in places where less able people rely on adequate fire safety measures - and are entitled to believe they are in place too.

I'll be honest, he's likely to get away with a hefty fine and community service - he should be locked up, but I doubt that will happen.
 
I notice too, that they've done him for "culpable neglect" - that's the lower of two possible charges. He could also have had a case made against him for willful neglect which would almost certainly have carried a prison sentence with it.

They're obviously going for the sure bet, so as to be sure of conviction.

Had anyone suffered as a result of his actions, he would have been looking at a minimum charge of culpable or attempted manslaughter.
 
Perhaps something about this can be posted in a General forum too - there's many guys out there in the forums who don't have access here who would benefit from knowing this.

Thanks!
 
Food for thought I felt.

The more awarenes raised over shoddy unsafe practices in all aspects of the electrical industry the better for those of us that do our jobs correctly.
 
Not a nice thing to see happen to someone especially a sparks(or so they say),if what they say was true then he can only blame himself,but was he qualified,im not so sure.
 
Why was he not aware of what he was supposed to be looking after.. was he looking or just taking the money...


When we keep looking at something we don't notice things as they become part of the furniture but I don't see how this could happen in a situation like that.

I would hate to forget something an leave a system substandard but to ignore things is something else. Obviously no check list.

Is this an example of complacency???
 
Last edited by a moderator:
I noticed when he was described,he was a firefighter,when he was the villain,he was an electrician,thats true to form

I am not defending the guy,but what about the duty of care of the person in charge of the premises
Its ok getting certificates aligned with cheap quotes,but they too have a responsibility,or are they innocent ?

I say that, because it smells of the same type of situation as someone doing a pir

The government will not make competence compulsory, yet expect the duty holder to employ someone who is a bit short on the competencey and only act,in this case, against someone who was allowed to practice,concluding with this tragedy

Why is policing of our industry and the selection of competence left with the individual,yet the consequences are bourne by the people in the industry

What a mess this industry is in
It is saddening to say the least
 
Damn. I posted further to this earlier, had a browser go slow, page loss, and just noticed the missive I wrote about this didn't show up.

I wanted to add some commentary on this, because it is important from so many perspectives.

One of the key points I wanted to raise, and why I feel this is better off in a general forum than tucked away in a "tight" group, has to do with the fact that above all, this is yet another example of the way we, in the UK, do NOTHING AT ALL about shocking disregard for fire safety until AFTER disaster has struck.

The vital point to all of this is, as I have said many, many times - it took (and I missed this initially) the loss of a person's life, for ANYTHING about this at all to be investigated properly.

To be perfectly honest, I'd love to go and slap Greater Manchester's fire chief around the head repeatedly for his own culpability in this matter.

Does that seem excessive? I don't think so - and he (and all other fire chiefs) know it as well as I do.

One of the great FAILINGS of the Regulatory Reform (Fire Safety) Order 2005 lies in the fact that it took responsibility for fire safety in buildings out of the hands of experts, and put it into the hands of people who cannot EVER be expected to understand the full implications of fire safety.

It was the biggest exercise in buck passing since the Spanish Inquisition. Quite simply, faced with massive underfunding, rather than fight, the fire service chief of the UK rolled over, and let the biggest travesty since Kings Cross happen quietly. They did not stand up and fight for the funding to continue to ensure that Fire Safety Officers had the final say on whether measures were adequate or not.

We now have a situation whereby almost anyone can call themselves a Fire Risk Assessor, offer fire safety consultancy, and carry on in the certain knowledge that if they SOUND credible, nobody will ever challenge them unless something like this case here happens.

This test case is both a good and a bad thing.

It is a bad thing, principally, because it highlights the very fact that the RRO is all about finding scapegoats, apportioning blame, and removing responsibility from the very people who ought to have held onto it.

It is a bad thing, because it highlights the fact that we are now in a position which, for all the very many faults of previous legislation, could not have reasonably existed before.

Were fire services still responsible for assessment, there is no way on this earth that guy would ever have got away with years of certification with the system in such a state. This highlights just how much MORE vulnerable we are to the risk of fire in public and multiple access buildings than EVER before (well, since we stopped living in caves, anyway).

It is, however, also a good thing, if it is used as it ought to be, for the public good.

And by that, I mean that this guy needs to be punished appropriately for his failings, and for the situation that occurred as a result of his criminally negligent behaviour.

However, the case itself *must* be used to highlight both the strengths and the failings of current legislation - primarily the RRO, and the impending train wreck that is BS9999, and building regulations not excepting.

It is past time, given that no fire legislation has ever been enacted prior to a major disaster, or loss of life, that we took proper and sensible action, and made LAW, the right to fire safety in buildings.

Before you all start telling me that there is law for this, you're right, and wrong. Much of the work so far done is valuable, but it is NOT enough.

The Building Regulations committee missed a golden opportunity with Part B. Other committees, the government, and the fire service have ALL missed opportunities - the RRO does not go far enough, and is already long overdue an overhaul. BS9999 was intended to streamline some of this, and other legislation. It is not, however, law.

The only possible benefit that can come out of this tragedy is that the case is used to properly highlight the need for qualified fire risk assessment, and commitment on the part of responsible persons to ensure fire safety is treated as it should be - life critical - to the lowest denominator - in simple terms, to reasonably accommodate the least able person ever expected to make use of a protected space. That cannot be achieved without mandatory use of fire detection and protection.

In an age where more and more costs are being cut, and front line services such as the fire service are being ever more squeezed, there can be no acceptable reason why the installation of sprinklers in ALL new buildings (domestic included) was not proposed to be included in Part B's review. That simple move, for the cost of less than 0.5% of the build cost, would cut the obligation on fire service response by over 80%, enabling them to become properly efficient, and to take back a duty they should never have given away.

Rant off, but boy, does the UK need to wake up to the implications of this, and other similar cases around the country.
 
Why was he not aware of what he was supposed to be looking after.. was he looking or just taking the money...


When we keep looking at something we don't notice things as they become part of the furniture but I don't see how this could happen in a situation like that.

I would hate to forget something an leave a system substandard but to ignore things is something else. Obviously no check list.

Is this an example of complacency???

I hate to say it, but it is a perfect example - IF THE FACTS ARE AS REPORTED - of allegedly qualified individuals thinking that fire alarms are simply a case of banging a few detectors up and all's well.

That, sadly, will be the mentality that led this individual to believe he could offer a contract, and that there was nothing to it beyond issuing a certificate each year.

The reality is, he probably didn't know any better, thought he was doing his customer a favour by shutting the noise up (if indeed it was him who removed the buzzer and not a previous company's "engineer"), and beyond the very basics, probably did not have any idea how to fix these faults, if he was even aware they were faults.

The real negligence lies in the fact that he should have been properly trained to deal with fire alarm systems, and properly aware of the risks of taking on such work - for himself and his customer.

Equally sadly, I think it is an example of ignorance, rather than simple complacency - though complacency also features, as the guy should have got off his coupon and done the training.

Fire alarm control panels are specifically designed to alert you to any fault on the system - that's a required part of the Standard (Part 4) - and the buzzer will NOT silence fully until the fault is fixed - nor will the AMBER coloured illumination extinguish until the fault is fixed. It is specifically designed not to be ignorable.

The fact that the buzzer was disconnected, and the light painted over was a willful act on *someone's* part to avoid repair to the system, either on the basis of cost, or on the basis of ignorance. No other explanation for it.

As for the replacement of fuses with wire - common though the practice used to be in the security industry to use a strand of 7/0.2 wire to replace a blown fuse on a temporary basis (one strand is broadly rated 5A), it should, IMO NEVER be done for ANY reason.

There's no excuse for any professional technician not to have replacement fuses about his tools and stock any time he is at work. Ever.

As for the component described as suspended between two terminals - that fire expert knows as well as anyone who's ever worked on a fire system that end of line capacitors and resistors are connected in such a way when the circuit is not in use - they are NEVER soldered to the PCB. That was an idiot point, if it was an EOL device (unless said device should have been in the end of line device on a circuit being used), and beyond sheathing the legs of the component, said expert would well know there is NO OTHER WAY of connecting said component.

It may be, of course that he was referring to a different component, in which case, it should be made more specific, primarily because hundred of technicians will now be panicking about EOL devices in control panels, wrongly.

Again, more than anything it is just another reason why morons like me wonder round telling morons like those, that fire safety is not a joke field, that beyond design, maintenance (proper maintenance) is essential, and why morons like me pray that one day this country wakes up sufficiently to enact appropriate legislation BEFORE another life is lost to fire.
 

Reply to Engineer To Be Sentenced in the Electrical Engineering Chat area at ElectriciansForums.net

Similar Threads

Hi there unsure where to ask so i have joined this forum hoping someone will know. I am currently employed by a large firm as a fire alarm...
Replies
7
Views
2K
Hello Ladies, Gentleman, Fellow Sparks, I'm Rob Argent, New to the site, Former 15th edition electrician now last 18 years Integrated Security...
Replies
4
Views
2K
I expect this bunch of blokes would not have got into as much bother if they hadnt bothered pretending to be NICEIC members and used the logo...
Replies
25
Views
4K
Two companies have been sentenced for safety failings after a worker was electrocuted during work on a data centre in Middlesex. Balfour Beatty...
Replies
0
Views
1K
A
DATA FACILITIES NEED NEW INSPECTION AND TEST ENGINEERS IN THE SOUTH & SOUTH WEST The Role of an Electrical Inspection & Test Engineer The ideal...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock