Discuss EV charger considerations on TT supply in the UK Electrical Forum area at ElectriciansForums.net

DaveS

-
Reaction score
24
Hi all. Will have to forgive me for enquiring about basic question but would rather be sure of all considerations than not. Went to view property for potential EV install yesterday. On viewing intake of property I realised supply had been converted from PME to a TT supply. I'm unsure why they may of done this? The property does have solar power, could this possibly have been a consideration why they converted this?

The whole install is protected upstream with 100ma RCD then to household dual RCD board. I took a quick ZS reading at intake and was 100ohms which is acceptable to me. My plan for EV as will be situated conveniently next to outdoor intake cupboard will be to split supply from 100 amp connector and from here take new supply tails to new dedicated EV A type RCD consumer unit and take my main earth from main earth block. In this situation there will be no 100ma upfront RCD. As not great deal of experience regarding TT installs just wondered if anyone thinks I'm missing any considerations here?

Thanks
 
HI DaveS, I see you didn't get much response on this but one comment think worth raising for future readers is the suitability of a the A Type RCD on a vehicle charging point circuit. In general the potential for DC Leakage/DC fault current may command at least a type AC or type B. Section 722 applies stating "at least Type A" but primarily requirements as stated by the manufacturer of the EV equipment should be followed. Does the particular EV charging equipment have protective measures against DC Fault Current? Type A probably doesn't cut it on DC equipment downstream and would be at risk of leaving the circuit without any effective RCD protection. I think the jury is still out and amendments being considered on DC connections.

As far as no upstream RCD on the supply, my current understanding would be I don't think this is an issue providing considerations to protect the meter tails are being met. Would welcome hearing from those most experienced in TT installations.
 

Reply to EV charger considerations on TT supply in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
741
I have a client who wants an EV charger installed, charger TBC, but about 7KW, installed about 20m away from this installation. I've not done one...
Replies
37
Views
3K
Hi All, Im quoting to install an EV charger (Dont worry - fully registered, but only been 2 weeks so i'm still picking bits up). Consumer unit...
Replies
1
Views
1K
I am an NICEIC contractor but I have never installed an Electric vehicle charger. I have watched all of the relevant NICEIC webinars (The wire) on...
Replies
18
Views
948

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock