Discuss EV charger issue - Garo PME trips in the UK Electrical Forum area at ElectriciansForums.net

https://www.digikey.be/htmldatasheets/production/2996418/0/0/1/dua55-datasheet.html

ElectricallyRandom - Please would you look at the section 'Range Settings' in the link above and tell me what voltage window and measuring range have been selected by the four little switches on the voltage monitoring relay behind the flap.
Apologies for a late answer - busy time. I've just checked and here's the settings. That should mean 230V +-10% according to the datasheet. What do I make of it... ?


ADCreHduBXm6GwyVfYZ53BVxm_DVoierMQseM7OaI_ehYQ6czVOYkFiO75VUuUW9K13oc6hcFX_wM1K89Lu637hZwzbklribV7LlxPDpzEzkszwZW77FUsxB4eL_1CogvErZ_vsc2QDQljDcuXb-xKIv5XMoIaVeAcvPRvfPJtUN45LVijXSsS9HaUV8-FLvtULjfhi180a92s8gFY_nBhpCgd7uwzOUqatoLJhB3Dk3CAgG2mAyn0uWlpYdo8DkDIQmmIZPEqeEVJr9nQ7Yy-kQG1qPMy79Nwt831MKkH6HoYa5bGHzhODBLTgVl0kSg2EAhKbKiG359DICJ7-fvtiIxXx9jLzxhPEGcpZd6wh-FZyg1UkPz9s90O8nGj4V9iwWr0dDMa_0trmAXnUd583rfjxVROjwDxirlP_3d9j5wB6HJIkzzwpHYzMtCk4M5HiM3VzPkXamT5brvgS4lj4FZ0eM0ctcT88zwJ4y-qBidyQvHaW0KBZNcZLS8FV7rB0z3C9ZW0pAXJ4SDcpHWgSrX_A6gzJmhFHo_dF-_BJCPzI3wuE-_H3fQsQ1NXEiHmosPu4Ri9Wb1eirFc2LQNRakjtEwumsYeljlGulGYkuEZP7tEyqlTOwY1zqiGZGtFsM3NG3KuYF-DEew-whUEdZ2shlzm1Bu7vHo3HSX827lqBKWCR_wo4ErM9TB2TbTTXSwQtKd5TYWW0tnTmtX7zh0sA8TDe-_es6qrgqae6v5wVfv05E0tw6Wi05URijhwOlf0iL4rSdn4nq-8P_CHTic5yC3LE6zc2T5mlJFIWaxz6pwa9xNqRfp8SSaGc7IIBY2GaJjOC844IhyIBuKx_iuAKWJrYdHwG650TgcsLkBOwyMj0syXcx0-0OXY1dPl86CCw_xXGk5r8bLB18w5NI72k=w1004-h1338-s-no
 
If the car is inside the garage there is no need for PEN fault protection. (From the Code of Practice)
I don't think its quite as simple as that. I think it's more along the lines of if the vehicle cannot be charged outside then there is no need for PEN fault protection (on PME or TNS system (as you have to assume TNS is actually PME and not a proper TNS) ). If the EVCP is installed in the garage and the car could still easily be charged outside due to the position of the charger then you still need PEN fault protection.
 
I don't think its quite as simple as that. I think it's more along the lines of if the vehicle cannot be charged outside then there is no need for PEN fault protection (on PME or TNS system (as you have to assume TNS is actually PME and not a proper TNS) ). If the EVCP is installed in the garage and the car could still easily be charged outside due to the position of the charger then you still need PEN fault protection.
Indeed. You worded it in a less ambiguous way.
 
For your interest, the heating effect of a 26A current is 66% of the heating effect of a 32A current since the heating effect of a current is proportional to the square of the current. So {26/32}exp2 = 0.66 x 100 = 66%

The RCBO contains an electro-thermal-mechanical trip which uses the current flowing to perform its overcurrent detection function.
 
ElectricallyRandom: Where are we going? If we find that the RCBO holds with a charging current of 26A then there is some evidence that a factor in the problem is the magnitude of the current and its heating effect. I suspect - don't know for certain - but either the RCBO is faulty as others' experience has suggested - in which case it is a simple one for one replacement, or that even with a new RCBO in place the real problem is that for the high long term charging current of 32A, the operating current of the RCBO is derated to a lower value than its marked 40A and less than 32A. If this is indeed the case what I would try next is to re-arrange the voltage relay, contactor and RCBO on the rail of the GARO box so that from left to right we had RCBO-Voltage Relay - Contactor. By doing this we move the warm coil of the contactor away from the warm electro-thermal-mechanical trip mechanism of the RCBO and thereby allow the RCBO to operate at a lower temperature which in turn reduces the amount of derating. We can then trial a charging current of 32A again. Does this seem like a plan if we find that at 26A the RCBO holds closed? You will have to call back the electrician to do the re-arrangement. It would be no more than an hour of his time.

I still think the 4mm2 cabling is too thin because the voltage drops as measured by the Tesla charger point are in my view excessive and power is being wasted warming them up. Typically 6mm2 would be used. But a simple solution is to double up the 4mm2 cabling.
 
ElectricallyRandom: ?????????? Did I contribute as others have in vain?
Oh yes you have 😃 I have dropped the current to 26A and last night on 3rd charge at lower current my pen device has tripped again. Just lowered the current down to 22A, but this is clearly not sustainable. I totally take your point on reshuffling the pen fault device's modules to help with heat, but it feels like a bit of hit and miss. I am very tempted to swap it altogether (would gladly just remove it tbh, but that's not quite right).
 

Reply to EV charger issue - Garo PME trips in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
851
Help please! I need a Tesla Gen 2 EV charger fitted in my garage which is 22m from the consumer unit. My electrician is proposing to route a 6mm...
Replies
15
Views
2K
I am an NICEIC contractor but I have never installed an Electric vehicle charger. I have watched all of the relevant NICEIC webinars (The wire) on...
Replies
18
Views
1K
Hi all, I've installed a Tesla Gen 3 wall charger supplied by my client. For your information, the place that I installed is in a block of flat...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock