Hmmm, having watched a Sparki Nija vid and a listened to a podcast (Oct 19) from e5 Group, seems the Amendment 1 gives 4 options for ev charging so apply them in simple terms for domestic property;
1) 3 phase, unlikely
2) Local earth rod, connected to MET. Again unlikely to achieve the required resistance
3) TT the ev charger
4) This new device for single phase, where voltage between Line & neutral is monitor and disconnected if it goes above 253V or below 207V.
The forth option in the Amendment, seems to be completely handed over to the manufacturer, to make it comply.
Then there's this thing about certain ev cars, and DC currents, requiring Type B or F RCD. And by the time Amendment 1 is approved, Amendment 2 will already be in draft!
Seems like this thing is going to be constantly changing/evolving. And a digital subscription with the IET.