I just wonder if the circuit the HF gear is on is mixed with old starter in another area. The two types do not get on well. Apparently transient voltages are not liked by HF. Is there any other gear around the (office/unit/warehouse???) that may cause a similar effect?
 
I dunno darkward, laughter eases the savage breast. Its just how far one takes it.
Yes it may but we have forum sections and open threads for such banter, my gripe is derailing someone else's thread and staff having to remove 12 posts that have nothing to do with what the OP posted and especially when he still online at the time replying and trying to answer questions put to him.
 
I just wonder if the circuit the HF gear is on is mixed with old starter in another area. The two types do not get on well. Apparently transient voltages are not liked by HF. Is there any other gear around the (office/unit/warehouse???) that may cause a similar effect?
No Vort, the whole place was refitted five years ago.

A mix of these TL5Cs and, T5s and some rare as hens teeth Phillips PL-R compact fluorescents. But importantly all HF.

It’s really only the TL5Cs that are failing.
 
Yes it may but we have forum sections and open threads for such banter, my gripe is derailing someone else's thread and staff having to remove 12 posts that have nothing to do with what the OP posted and especially when he still online at the time replying and trying to answer questions put to him.
Can someone delete these distracting posts that are explaining why distracting posts are distracting. ;-)
 
Ha, no not that stupid. They’re the 40W flavour TL5Cs.

Well I say that but the ones I’ve been replacing with are 40W, went of the label rather than the old lamp. Can’t say I checked what the duds were. Now they’re in a coffin at the wholesalers.

Number three on my to do list, check all existing lamps are correct.

Keep these coming I might stretch this out till Friday. :-0
Ok might sound silly or too easy but the TL5C is rated for 22-42w they aren't putting in the 17w lamps maybe, no couldn't be.
 
Yes it may but we have forum sections and open threads for such banter, my gripe is derailing someone else's thread and staff having to remove 12 posts that have nothing to do with what the OP posted and especially when he still online at the time replying and trying to answer questions put to him.

Thing is, in real life we have a laugh & a joke, whilst working, discussing serious issues, even when we are feeling low. We don't just wait for the proper moment, or limit it to special occasions . Its all part of life's rich tapestry.

Even the OP's enjoys the banter. Hope I'm still here tomorrow, in the literal sense. :D
 
upload_2018-8-30_8-46-3.jpeg


soz. thought you said bantam.
 
Well, not a very productive day.

All voltages 235-240 and stable as far as I can tell without long term monitoring. Checked every Click distribution box and at one fitting per box, with the lights on.

Did not see a PIR switch whilst there and apparently someone else had set them all to 30 mins which looks ok.

All lamps correct, of the random twenty I checked .

Did find three old fluorescents in the ceiling void that were on. These have been unplugged from the Click boxes.

This does not appear to be a deterioration issue as the maintenance records show a pretty steady rate of failure from installation.

The ballasts are Tridonic so not crap only question left is whether they are compatible with the TL5CS, which I have to call the manufacturer tomorrow.

Hopefully there’s a picture attached showing the ballast.

7B42B45E-DD05-4E0D-A8C0-F042FE266AD3.jpeg
 

Reply to Excessive??? Compact fluorescents failing. in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock