Discuss Existing Supplementary Bonding in the UK Electrical Forum area at ElectriciansForums.net

upload_2018-1-8_19-7-32.png
one of them alterations to the bathroom circuit .
 
I have clarified this particular point before wid' my scheme. If there are no alterations to the circuits, replacements are like for like, then there is no requirement to install additional protection.

Imagine if you replace a pull cord, sorry Madame I now have to install you an RCD FCU.

Now what about that towel radiator?
 
You could put one in front of the CU, would be easier than faffing with the bathroom circuits, I would think. Still think he is wrong to use the 30 Amps in his calculations. In the video CK is using 10ma as quoted in GN3 not a current that operates an RCD 230/.01 (10ma)= 2300ohms minus the resistance of the body ohms1000, in that calculation there is not any reference to the operating current of any OCPD, only referring to GN3.
The formula given to determine the effectiveness of supplementary bonding in bs 7671 is 50v /Ia ( or I delta N when the circuit is protected by an rcd) to effectively make sure the touch voltage will not rise above 50 volts during a fault as long as the resistance of the pipework is below in this case 1.666 ohms.
So how is it wrong?
That video is for determining pipework is an extraneous conductive part like your water and gas services to see if they require protective bonding.
 
Last edited:
I would use the highest rated device on the installation as a fault occurring anywhere in the property could impact the bathroom.
 
The formula given to determine the effectiveness of supplementary bonding in bs 7671 is 50v /Ia ( or I delta N when the circuit is protected by an rcd) to effectively make sure the touch voltage will not rise above 50 volts during a fault as long as the resistance of the pipework is below in this case 1.666 ohms.
So how is it wrong?
That video is for determining pipework is an extraneous conductive part like your water and gas services to see if they require protective bonding.
No the video is explaining how to test pipework to see if they require any supplementary bonding, there are other tests to ascertain that main bonding is up to scratch.
 

Reply to Existing Supplementary Bonding in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Curious about supplementary bonding, I have these two 4mm Cables loose and not connected to anything in my parents house. I presume they are for...
Replies
9
Views
2K
Hello. Non-electrician here. Failed an EICR yesterday as the electrician graded my consumer unit C2. Why C2 and not C3? He didn't say (and still...
Replies
22
Views
3K
Just had my design project handed back to me from my last block and I got everything right apart from one question Q9 I would take a photo but...
Replies
3
Views
1K
One of the oddest jobs I've ever had today. Called by a plumber I know who had attended after a leak through the kitchen ceiling from bathroom...
Replies
24
Views
6K
Hi, Small flat, currently has a small'ish feed water tank, top of a cupboard, feed through a wall into under stairs cupboard. Hot water tank...
Replies
5
Views
469

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock