Discuss Existing Supplementary Bonding in the UK Electrical Forum area at ElectriciansForums.net

Hurry up, I've got to go to bed soon, and I don't want to be thinking about this all night!
No nor me, can't sleep very well as it is, That's me done said my piece I believe I am right, good night all.
 
That is not what bs 7671 says on the matter.
It’s the protective device for that particular location

But the test or concern is between exposed conductive parts & extraneous conductive parts in that location?

Having reread the OP I now realise the towel rail is fed from the boiler and not electric.
 
Hurry up, I've got to go to bed soon, and I don't want to be thinking about this all night!
MV5BMTQ2MjMzOTczOF5BMl5BanBnXkFtZTcwMTU0MTgwNA@@._V1_.jpg
 
reg 415.2.2

"where doubt exists regarding the effectiveness of supplementary equipotential bonding, it shall be confirmed that the resistance R between simulataneously accessible exposed-conductive-parts and extraneous-conductive-parts fufils the following condition:

R less than/equal to 50 V/Ia in a.c systems

Or in the case of an rcd
50v / I delta N
 
reg 415.2.2

"where doubt exists regarding the effectiveness of supplementary equipotential bonding, it shall be confirmed that the resistance R between simulataneously accessible exposed-conductive-parts and extraneous-conductive-parts fufils the following condition:

R less than/equal to 50 V/Ia in a.c systems

Or in the case of an rcd
50v / I delta N

So towel rad pipe at 0.04ohms, doesn't require local supplementary bonding?
 

Reply to Existing Supplementary Bonding in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Curious about supplementary bonding, I have these two 4mm Cables loose and not connected to anything in my parents house. I presume they are for...
Replies
9
Views
2K
Hello. Non-electrician here. Failed an EICR yesterday as the electrician graded my consumer unit C2. Why C2 and not C3? He didn't say (and still...
Replies
22
Views
3K
Just had my design project handed back to me from my last block and I got everything right apart from one question Q9 I would take a photo but...
Replies
3
Views
1K
One of the oddest jobs I've ever had today. Called by a plumber I know who had attended after a leak through the kitchen ceiling from bathroom...
Replies
24
Views
6K
Hi, Small flat, currently has a small'ish feed water tank, top of a cupboard, feed through a wall into under stairs cupboard. Hot water tank...
Replies
5
Views
469

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock