Discuss Extending ring final circuits in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
12
Hi. I have a CU move to do - around 5m from current location. There are 10 circuits, 4 of them ring finals.
I'm considering whether to extend the rings 'as are', or to split the rings somewhere in their approximate middles and extend them to separate RCBOs as radials, the aim being to reduce the effect on the installation of any individual RCBO trip.
Seems like a plan to me - although it doesn't reduce the amount to cables to be extended and does add labour in identifying the rings.
Am I missing anything?
 
If there are tripping issues that is driving this decision then there are other circuit problems that need attention and priority
If there are no tripping issues,same as Andy "a lot of work for little or no benefit
You may also have to assess the would be radials to be better balanced for likely use than just breaking at the centres
 
Hi. I have a CU move to do - around 5m from current location. There are 10 circuits, 4 of them ring finals.
I'm considering whether to extend the rings 'as are', or to split the rings somewhere in their approximate middles and extend them to separate RCBOs as radials, the aim being to reduce the effect on the installation of any individual RCBO trip.
Seems like a plan to me - although it doesn't reduce the amount to cables to be extended and does add labour in identifying the rings.
Am I missing anything?
are you moving CU or fitting new? if new will it be dual RCD or RCBO?
 
hen fit a din rail box in current CU location and extend cables as is. i.e. preserve the 4 RFCs. to make life easier, you could run 6.0mm from new CU to each RFC in the din rail box. so you'd have 4 x 6mm instead of 8 x 2.5mm from CU to din rail. basically lollipop circuits,
 

Reply to Extending ring final circuits in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Evening all, Been to a job on Fri where the customer had a condition report completed. Two of the remedial identified was that there were too...
Replies
7
Views
1K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
729
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
814
Hi all looking for some advice as a non sparky , be gentle :) To be clear I wont be doing the work myself , just want to be better informed. I...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock