I do occasional soldering in my garage and would like to add extraction for the fumes.

I already have a Bathroom Extractor Fan Kit lying about (Fan, Ducting, Vent, DP Fan Switch etc) so looking to put them to use, my question is these are normally wired from the ceiling rose and use the S/L within that to activate the fan.

I would like to just have the Fan as its own separate circuit with a single On/Off switch, Does anyone see an issue to wiring the Fan up as follows..

Feed (3a FCU) Cable: 1.5mm Twin & CPC >> DP Switch (Live + Switched/Live Looped at the switch, fan side) Cable: 3 Core & CPC >> Fan

Happy for opinions and criticism :)
 
You only need a two core and cpc to the fan just fit a link across the two live terminals.
 
You only need a two core and cpc to the fan just fit a link across the two live terminals.
Thank you, another member has also suggested this, it does make sense now it has been said i was just thinking of using what materials i already have
 

Reply to Extractor Fan for Soldering in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I’m replacing an old 100mm extractor fan in the kitchen with a new one. The old one was a pull cord fan whereas I bought a timer one (no pull...
Replies
3
Views
408
Hi all, I'm in the UK and have recently had a ducted extractor fan Mixflo 200W with timer fitted. The fan comes on with the pull cord and runs for...
Replies
6
Views
326
I've installed a replacement bathroom extractor fan. Pic on the left is the old one. Pic on right is the new one. Wired the same way but the fan...
Replies
4
Views
956
Hello, I'm swapping my extractor fan in the UK and I have bought a Turkish extractor fan stupidly and the connections you can see in the picture...
Replies
1
Views
436
Need to replace an old Vent-Axia extractor fan as the pull chord no longer works. I bought this -...
Replies
19
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock