Discuss Extraneous conductive parts in outbuildings in the UK Electrical Forum area at ElectriciansForums.net

soulman

-
Arms
Reaction score
94
Hi, i am after a bit of advice. I went to a property which had 3 outbuilding, all were separate from the main building, one garage, one shed, & a workshop. Circuits all supplied from main building. Earthing system is TT. In all of the 3 outbuilding there is a separate water supply with metallic pipes. There is one socket outlet & one light in each building.

My question is, should these pipes be supplementary bonded? or would they need m.p.b to the MET.

cheers
 
Are the metallic water supplies extraneous? They might seem metallic but they're often fed in plastic. If they are extraneous, are they continuos from the main building to the outbuildings? If they are, are they bonded at the main building?

A few different scenarios and solutions here:

1. The water pipes are not extraneous - They need no bonding.

2. The water pipes are extraneous and are not already bonded (for example a completely seperate water supply or there is plastic between the main building and the outbuilding but enough copper in the ground to make them extraneous) - They need bonding back to the MET at the main building if you are extending the equipotential zone or bondng back to the outhouse MET is you are creating a TT system.

3. The water pipes are extraneous but they are effectively connected to earth already via the MET at the main building - They need no additional bonding, however supplementary bonding may be prudent.
 
You need to do two things.

First, disconnect the main earthing conductor from the MET at the main building and test between the incoming water pipe and the main earthing conductor. This will determine whether it is extraneous, anything less than 45,000 ohms and it is.

Second, with the main earth still disconnected, long lead test between the water pipe at the outbuilding and the incoming water at the main building (remember to null the lead!), anything around 0.05 ohms or less and it is effectively connected to earth throughout its entire length.

If the incoming water pipe at the outbuilding is effectively connected to earth, no further bonding is required, however I would personally still add supplementary bonding at the outbuilding.
 
There should be still MPB installed at each building locally, to an EMET (411.3.1.2) applies (taken from GN8), providing it is an ECP of course.
 
You need to do two things.

First, disconnect the main earthing conductor from the MET at the main building and test between the incoming water pipe and the main earthing conductor. This will determine whether it is extraneous, anything less than 45,000 ohms and it is.
With the 45KΩ you are aiming for a 5mA safe current, what is the basis of this level of current?
Perception is lower and let go is higher, is this just a very safe level?
 
If the incoming water pipe at the outbuilding is effectively connected to earth, no further bonding is required, however I would personally still add supplementary bonding at the outbuilding.

You'd be a bloody fool not to bond any metallic extraneous earth entering a stand alone building, whether it had been bonded at say the main house or another building or not!!. Call it whatever you like supplementary bonding, main bonding or whatever!!

Same goes for blocks of flats, every flat should be classed as a separate entity, as far as main bonding of extraneous metal pipework etc is concerned....
 
If an earth potential is introduce to the building because a metallic service enters then it should be bonded.
If the metallic service later passes into the ground again as it leaves the building it is also introducing an earth potential at that point and so should be bonded there.
However if it is continuous I would not bother, but if someone replaces some of the internal pipework with plastic then there could be problems.

Perhaps
 
Hi, I have managed to find my GN8. The separate buildings ECP do require main protective bonding back to the MET in the main building. I thought supplementary bonding would suffice, but the book says not.

Thanks for your help.

P.s Cheers to spark 68
 
You'd be a bloody fool not to bond any metallic extraneous earth entering a stand alone building, whether it had been bonded at say the main house or another building or not!!. Call it whatever you like supplementary bonding, main bonding or whatever!!

Same goes for blocks of flats, every flat should be classed as a separate entity, as far as main bonding of extraneous metal pipework etc is concerned....

Well that was kind of my point lol.

It would be supplementary if already bonded and yes, you would be a fool not to IMHO
 

Reply to Extraneous conductive parts in outbuildings in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
During an EICR I have come across a metal tap and copper pipes supplied by a blue plastic pipe. This measures 0.022 MegOhms, this is directly...
Replies
24
Views
3K
During an EICR I have found an isolator with no cpc present bolted to a large metal post and all the motorized metal car park gate, the fact that...
Replies
22
Views
3K
Hello, Carrying out remedial work on a commercial site and I've come across a metal out building that has a water supply to it. The water pipe...
Replies
6
Views
1K
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock