Fault finding on ring final, is this the readings you would expect to achieve and are these the correct way to find them thanks
Discuss Fault finding on ring final circuit in the UK Electrical Forum area at ElectriciansForums.net
Fault finding on ring final, is this the readings you would expect to achieve and are these the correct way to find them thanks
View attachment 38835
View attachment 38836
Are you a trainee, electrician or a DIYer as your profile is a little sparse.Fault finding on ring final, is this the readings you would expect to achieve and are these the correct way to find them thanks
View attachment 38835
View attachment 38836
3rd year apprentice don’t do much fault findingAre you a trainee, electrician or a DIYer as your profile is a little sparse.
Then to aid us in helping perhaps you could update your profile and avoid unnecessarily obtuse answers.3rd year apprentice don’t do much fault finding
3rd year apprentice don’t do much fault finding
I'm guessing here but my guess he is his employerYou need to raise this with your employer ....... Fault finding is a key skill, learnt on the job, from others .....
I'm guessing here but my guess he is his employer
Well what's your take, the OP Could be doing a private job.Are you suggesting the apprentice is the boss?
Have you looked at the video yet? that should help know end, not much of a Boss if you feel you can't ask him a question, decent people won't mind answering a legitimate question. Where are you based? Sorry missed that London too far for me to come and help you out.I don’t fault find at work so pointless asking my boss and it’s for AM2 in few weeks and college have too many people to bother about showing me
Yes I’ve watched it, just wanted to know as in AM2 your only allowed continuity tester so all faults are wiring it’s just the same as dead testing just wanted to know if my drawings was correctHave you looked at the video yet? that should help know end, not much of a Boss if you feel you can't ask him a question, decent people won't mind answering a legitimate question. Where are you based?
Thanks so open circuit connect at board end eg. L+N then test at socket between L+N if I get reading OL then open circuit or can do end to end on each socket eg test L to L from socket 1 to 2,Pete's approach above is the best one, it will catch most faults, but as you only have a continuity tester:
Reverse polarity:
Normally easiest to find by inspection.
Assuming you have correct end to end resistance results, Joining two poles at the board one of which is not the expected reversed polarity and testing at the socket fronts should give one socket with OL result all others should be very low resistance.
Your diagram and method will work.
Open circuit:
discovered by end to end testing, join one non continuous core to a continuous core and test between the cores at each socket, when you get OL result this is where the fault exists (or the socket beforehand on the outgoing core).
Your diagram and method will work so long as only one leg is joined.
High resistance:
Similar method to open circuit but where the resistance rises is where the fault is (or the socket before hand).
Your diagram and method will work.
Short circuit:
testing between disconnected cores at board the low resistance reading indicates the faulty cores, break the ring down half and half again testing each time between the faulty cores until the fault is narrowed down.
Your diagram and method will not work. only the bit about breaking the ring applies, adding another short circuit to the circuit will not help.
Thanks that’s my problem cause I don’t do much fault finding I just over think itdon't over think. thast's a major problem.
a ring is just that. . 3 pieces of wire. you have 3 bits of wire with both ends at the CU. end 1 should connect to end 2, and not connect to the others. sssssimplesss.
No such animal as r1+r2 It's R1+R2 which is the figure of 8 reading after you have done end to end r1,r2 and rn and inter connected the conductors as per the video instructionsThanks so open circuit connect at board end eg. L+N then test at socket between L+N if I get reading OL then open circuit or can do end to end on each socket eg test L to L from socket 1 to 2,
Short circuit, so break ring in half then test end to end at each socket no r1+r2 as this is just adding another short circuit
Reply to Fault finding on ring final circuit in the UK Electrical Forum area at ElectriciansForums.net