Discuss Fault on ring main in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

D

dutchy

Hello everyone, I'm just looking for advice on a ring main fault, I'll try and keep the scenario short so as not to bore you al....

I was asked to attend this fault at an on going job our firm our firm is doing (I wasn't involved from the start) The existing kitchen ring had been broken into to incorporate a new utility room a few weeks ago. I was asked to attend a fault on the washing machine tripping out the ring.
The ring main works fine "under load" (dishwasher/tumble dryer etc) but when the washing machine is plugged in to its single socket under the worktop it takes out the mcb, but plug it in anywhere else and it works fine. (eliminating the appliance) I disconnected the leg from the spur to the single socket, and as i was testing for voltage live/neutral was fine but when testing live/earth it takes out the mcb? (I'm returning on monday as I didn't have my test kit with me)..... now without having to start stripping the ring down, does anyone have any advice on a quick way to find this fault. The house in currently having renovations done, so its possible its a damaged cable, but found it unusal that all the other appliances are working fine, without causing it to trip.....any advice would be greatly appreciated.
 
I would say your getting terminologies confused here and it is taking out the RCD/RCBO rather than the MCB.

I simply say this because I think you have a polarity issue on the circuit. Either somewhere in the split you have crossed an Earth/Nuetral or more likely at the CU your on 2 different neutral bars.
 
Thanks everyone.... its definitely taking out the MCB... its a split load board, and the RCD stays on....only the breaker goes.
 
thats the thing though...the washing machine is currently plugged in to a D/S on the same ring and its merrily working away fine, but when plugged in to its dedicated S/S via its controlling spur....pop it goes!...and its definitley not the leg between the spur and socket...already checked that...??????
 
I can never understand people attending faults with no test gear?? If you don't have test gear it's going to be very hard to fault find. I find it best to bring my test gear with me always. It's needed for all jobs anyway. Testing new installs as well as fault finding.
 
some people arnt as rich as you hawk1, they have to do caveman method and break ciruit up accordingly.. oj..

you should have it with you. as you are ment to test before installing anything and after..... but we know it doesnt happen in all cases or any at all..


what about this one was called to a fault few weeks ago in garvagh, the outside lighting wasnt working.. now i was witha spark helping him just, so letting him take lead role.. we walked around the perimeter to see circuit route and seen it split and went down a walkway to gate for a lampost floodlight. so went to middle of circuit and disconnected the live of one side and tried the the old mcb and still tripped and tried the other side and still tripped, so investigated on and we had found somone had added other lighting around the building frame itself. so opened contactor and seen one incomming and 3 or 4 out going circuits dont know where the neutrals were take too.. so disconnected one out going at a time and found the ciruit the fault was on and it turned out to be a ballast blown and causing a short... now this guy had no test gear, how would test gear of helped him here....
 
How can you be sure its not the spur leg if you have not tested it?

Does it trip with another appliance plugged in say a kettle!

I would start from the beginning once you get your gear and fully dead test the final ring and see what results are found for starters!!!
 
I can never understand people attending faults with no test gear?? If you don't have test gear it's going to be very hard to fault find. I find it best to bring my test gear with me always. It's needed for all jobs anyway. Testing new installs as well as fault finding.

the job is 100 miles away from our office, and I was passing it to get to my job (where my test kit was) which is why I have to return on monday...just didn't want to bore you all with that detail...
 
fault appears to be in kitchen... cupboards fitted... kitchen fitters..... 4" screws directly above socket?????
 
How can you be sure its not the spur leg if you have not tested it?

Does it trip with another appliance plugged in say a kettle!

I would start from the beginning once you get your gear and fully dead test the final ring and see what results are found for starters!!!

I completely disconnected the spur leg, so I just had the supply connected to the spur, and thats where I was testing live/earth and the MCB was tripping...
 
and when load applied bang, legs up, lights out

nope!...the ring is already under load with dishwasher/tumble dryer etc.... but as soon as you add the washing machine...pop!... but the machine works fine went plugged in to another part of the ring.
 

Reply to Fault on ring main in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
483
Hj our washing machine tripped out electrics the other day. Everytime we switched it in the electrics cut out. We noticed a larger bend in the...
Replies
0
Views
443
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
Hope you're all well . I've had ring door bell 2nd generation hardwired for 1.5 yrs... it was connected to transformer which is connected to the...
Replies
22
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock