Discuss Fault on socket circuit in the UK Electrical Forum area at ElectriciansForums.net

G

Grant McLaren

I am puzzling over an intermittent fault on a ground floor/kitchen socket circuit. Initially it seemed as soon as the oven switched on the RCD would trip. However, after unplugging the oven, I used a socket tester on other sockets, which would sometimes trip the RCD. It's pretty random, sometimes it will trip as soon as you plug something in, other times not. Zs reading were fine. The ring main has been broken, although the earths are still continuous. From what I saw, the socket circuit has not been done well.

When I left the property yesterday everything was on, but I'm waiting for a call from tenant to say it's tripped again.

Any thoughts on what it could be and why it has suddenly started now?

Regards.
 
So you have used a socket tester for fault finding and left a RFC with no continuity on it?
Looks that way Mate, makes you wonder sometimes. OP just be clear on this point did you do any IR testing, R1+R2 testing how did you conclude that the Zs is compliant?
 
Lol you guys are funny.

Used installation tester for testing. My point about the socket tester was that it and other nearby appliances, i.e., router or toaster would trip the RCD when I plugged it, but only occasionally.

The question is what could cause this and why? If there was a break down in insulation between, say earth and neutral (which is possible, since a continuity test between neutral and earth on one end of the broken ring at the CU gave me around 13 ohms, why wouldn't the RCD trip all the time and instantly?
 
Ring Final Circuit, Ring Main is no longer used, it's old hat, it is no more, Ring Main is Dead, RIP Ring Main, with your quals you should,or ought to be aware of that fact.
I do know what ring final circuit is, I just haven't heard it referred to as RFC.

I didn't know that ring mains weren't used anymore, although I independently stopped using rings ages ago. Whenever, I encounter an old ring, I assume it is broken and downgrade to 20amp.
 
You say you have continuity beteeen E-N, that may not trip if the current still finds a return path on the neutral which wouldn’t trip the RCD
 
You say you have continuity beteeen E-N, that may not trip if the current still finds a return path on the neutral which wouldn’t trip the RCD
I didn't know that ring mains weren't used anymore, although I independently stopped using rings ages ago. Whenever, I encounter an old ring, I assume it is broken and downgrade to 20amp.

Why do you assume that? Testing the circuit correctly will verify wether it’s good for continued use, not guess work on your part.
 
Wha tests did you carry out and what were the results from then tests?
Zs 0.9ohm was about this highest reading.
tested continuity between line, neutral and earth, I guess this is a form of IR test.
And opened up most of the sockets for a visual inspection. Apart from a few loosely tightened terminals, which are now tight, all seems fine.
RCD is working as it should.
Didn't do a R1+R2 test (although I should have), but let's assume there is something wrong here, why would it only now start presenting problems, when nothing in the installation has changed.

One final thing, I'm anticipating returning the property to get this sorted, but I thought first I'd get some thoughts from some friendly sparks. At least I found some sparks.
 
New posts

Reply to Fault on socket circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
666
Hi all, Gone to look at a intermittent ground floor sockets fault today, the RCBO was tripping at random times with no pattern. Nailed down a...
Replies
11
Views
1K
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
331
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock