Discuss Faulty RCCB on old TT system in the UK Electrical Forum area at ElectriciansForums.net

E

edrobbo8

I have a problem to sort out - it is a TT system with a faulty 80A 10mA RCCB after the meter and before the consumer unit. The board is very old style MCBs with no RCDs present.

The customer called me up because until about 6 weeks ago the front garden lights were causing the RCCB to trip. I went round to look at it and pressed the push to test button and it worked, plugged the Megger into a socket and it would not trip it on x1 or x5, the ramp test did nothing either.

So, to comply with current regs, can this faulty RCCB be replaced with a similar unit, or is it a new board?
 
nothing to stop you replacing the RCCB. it's classed as maintenance. and why 10mA? are you sure it's not 100mA and you've typo'd or misread?
 
Sraight swap for a 30ma to get out of trouble.....new CU with up front S type and RCBO's in an ideal world.

Edit.....just a thought...is there actually an earth?....if it trips on the test button it should operate with earth leakage. What was the Ze/Ra?
 
Ze was 98 Ohms, so reasonable considering dry weather (this was a week or so ago). I am fairly certain it was 10mA which I thought was strange, but was in a rush so could have been 0.1A! Going back there on Saturday so will double check. Ideally yes new CU but money money money!
 
The old RCCBs only reacted to Live to Earth Faults (see the diagram inside the terminal cover). The test button connects a resistor across live and earth which energises the trip coil and switches off the power. I believe an RCD Test leaks current between neutral and earth, so won't trip an OLD RCCB. :smart:
 
Last edited:
I was going to replace with a Wylex insulated enclosure and DP 80A 30mA RCD.

You shouldn't really be replacing an old CU with a new one that has only 1 RCD.
If you want to replace it, then do so with either a high integrity board or a dual RCD board. Better still, and if space is limited, a board with a 100mA S-type main RCD and 30mA RCBO's.
 
Thanks Guitarist, I was going to replace only the faulty RCCB with a 30mA RCD to cover the whole installation - as telectrix said it's maintenance! If I was replacing the whole board then I would use a split load board with dual RCDs.
 
Thanks Guitarist, I was going to replace only the faulty RCCB with a 30mA RCD to cover the whole installation - as telectrix said it's maintenance! If I was replacing the whole board then I would use a split load board with dual RCDs.

Not a particually good idea on any TT installation!!

Guitarist ...Better still, and if space is limited, a board with a 100mA S-type main RCD and 30mA RCBO's.

A much better protective set-up where a TT system is employed!!!
 

Reply to Faulty RCCB on old TT system in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
Hi all,looking for some pointers to an RCD problem, I work entirely on large poultry farms, I've only been in post a year, at some point before I...
Replies
6
Views
2K
Doing one more of the flood of EICR today on a rented property before a tenant change, but ran into a slightly interesting case so would...
Replies
71
Views
13K
....To fit old Sentry board. Present board has 80A, 30mA RCD mainswitch, and it’s a 16 way board!! I can’t get all circuits to stay on all at...
Replies
19
Views
5K
I have a replacement consumer unit coming upon which is currently off a TT system with a nice low reading on the earth. There is no chance of the...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock