Discuss figure of 8 test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
5
Can someone please explain why we have to cross conductors from legs of a ring to perform figure of 8 test (r1+r2 or rn+r1) and why we can't just link those conductors from the same leg as it would also make a loop... Would I be right in thinking that you would get a more even reading across both conductors when connected in figure of 8. Rather than the way I said as it would measure a much shorter distance. And would give inaccurate readings?
 
not only that, but by cross connecting, all your outlets should give the same value for R1+R2, unless there;s a spur off the rfc.
 
As tel said, easy way to locate spurs and loose connections.
If you don't connect them to opposites they will go up as you go along the ring then back down.
Like your loop readings will.
 

Reply to figure of 8 test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All, Had a weird one this morning during an EICR. Testing a ring final circuit in a 2 bed flat… kitchen was on a separate ring. With only the...
Replies
7
Views
1K
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
833
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
605
After fixing a few CPC related issues on a ring final I got the following results L-L = 0.47 N-N = 0.47 CPC-CPC = 0.69 R1+R2 Tested at 0.31...
Replies
3
Views
1K
Hi so i am doing a test on sockets on a ring Final circuit for family member. Got my end to ends r1 0.62, rn 0.64, r2 0.97, identified opposite...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock