Had niceic guy out today and has advised that behind kitchen units i dont need to fit fire rated clips in trunking. I was under the impression that they were to be fitted in all trunking? Any thoughts?
Discuss Fire rated clips in trunking in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
because in that location, due to a fire, perhaps, fallen cables will not pose a hazard
Think that's a good answer, all that's needed really.because in that location, due to a fire, perhaps, fallen cables will not pose a hazard
I thought they had to be fitted in all trunking as per 18th edition?
I thought they had to be fitted in all trunking as per 18th edition?
I am aware that it does not come into effect until 01/01/19 , but i have the new book and want to adhere to it from now on.
Once again as previously stated got to consider the proportional risk involved.From january and there is a piece of plastic trunking to be fitted, for whatever reason, in a sitting room 300mm from the floor from 1 wall to the next wall.
Would you fit fire rated clips inside or would you say that there is a reduced risk of entanglement because of the height of the trunking?