solarman73

Hi Guy’s
We have a contract to fix 50kW of panels to a barn roof. Having problems finding a suitable fixing/ racking systems to use without having to build lots of support under the roof. Eaves to ridge is approximately 14meters with 9 Z shaped steel purlins spaced equidistant between eaves and the ridge. The main steel beams are spaced approximately 5-6 meters apart.

Any ideas would be grateful.
Inside Barn.jpg
 
I used the K2 system on one I did recently. that was into wooden joists but they also do coach bolts for steel which then have a rubber cup on them to seal the hole. seemed to work pretty well.
 
We did it by replacing the J bolts holding down the wavy roofs sheets with much longer stainless steel J bolts and then using Renusol brackets. New rubber seals etc and stainless nuts.
You will need a test report of structure, weight, calcs, etc etc etc , our cost over £500 but proved roof needed no additional structural work.
We managed to cut out the existing very rusty J bolts with angle grinders. Scaffold outside and tower inside.
Long walkboards on roof and NO broken or cracked concrete or absbestolux or whatever they are sheets . Result
 
Last edited by a moderator:
Hey Guys

Thanks for the replies so far. They have been very useful.

The roof is not asbestos thankfully so we don't have any problems with drilling.
 

Reply to Fixing panels to a barn with a concrete fibre roof. in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hi Guys , I was just keen on your proffered thoughts for fixing Solar PV Panels to a fibre cement roof. We have metal Z purlins to fix to at...
Replies
3
Views
2K
Earthstore
E
M
Any know of a solution for mounting panels on a fibre cement roof that has concrete beams/purlins underneath? The bolts that hold the roof down...
Replies
6
Views
9K
W
Hi We are currently looking at an install on a barn roof that has corrugated 'cement' sheeting on it and we are wondering what is the best way to...
Replies
24
Views
7K
powervan
P

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock