Put on an additional snubber and re-draw your sketch.
Mike, please see a better diagram. I have now fitted two capacitors (only have 2) and no change. I would have thought two capacitors and a gu10 should quash any stray V? As soon as I disconnect the timer SL the flickering stops. Can I fit a 10a 250v diode to stop any voltage leakage back from the timer SL to the SL connection at the light switch, which is the only way I can see and voltage getting to the LEDs.
 

Attachments

  • Screenshot_20230805-191921_Gallery.jpg
    800.3 KB · Views: 16
Can I fit a 10a 250v diode to stop any voltage leakage back from the timer SL to the SL connection at the light switch, which is the only way I can see and voltage getting to the LEDs.
It's ac mains. A diode will just rectify it, the result of which probably won't do what you want!
Is the S/L from switch to timer accessible? Would it be practical to use a 2 pole light switch and switch the timer S/L separately from the LED's? That would obviously stop the problem!

Could you confirm if the GU10 is LED or halogen. If LED could you try a halogen?

Sorry about all the questions - your circuit diagram rather neatly separates the wiring of the timer and fan from the wiring of the lights, but in reality are the physical cables jumbled together? That could lead to an induced voltage being the problem.
But if they are actually separated, I'll stick with the suggestion it might be the timer creating the voltage.
 
Last edited:
It's ac mains. A diode will just rectify it, the result of which probably won't do what you want!
Is the S/L from switch to timer accessible? Would it be practical to use a 2 pole light switch and switch the timer S/L separately from the LED's? That would obviously stop the problem!

Could you confirm if the GU10 is LED or halogen. If LED could you try a halogen?
The gu10 is a halogen, which I thought would sort any voltage leakage.
 
Thought it might be worth measuring voltage on Manrose S/L, both connected and disconnected.
Also try Mike Johnson's suggestion above.
Good morning everyone. As mike suggested I disconnected the SL at fan - no change.
I have fitted a different timer - no change.
Cables are not particularly close or bunched - so I think unlikely it's inductive from an adjacent cable.
Showing between 7v - 11v between L/N at one of the LEDs.

I have wired a pendant with 100w lamp across one of the LEDs L/N and problem gone, but obviously I can't keep that there!

I'm using .47uf 100r capacitor as snubber, but are these large enough (or whatever), as the 100w lamp appears to be able to dissipate the stray voltage.

Yet again I appreciate all the help.
 

Reply to Flashing LEDs when fan and lights off in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, have an old bathroom fan. Which has two wires the black and red (line and neutral). The fan has no isolator switch and was powered when the...
Replies
3
Views
700
Thinking a 240V AC relay activated by two independent light switches could be used to switch power to a shared inline extractor fan. The fan...
Replies
31
Views
2K
Need to replace an old Vent-Axia extractor fan as the pull chord no longer works. I bought this -...
Replies
19
Views
1K
Hi all, any advice would be greatly appreciated. Went to do some work at a factory unit on Monday ( changed 20 florries to LED battens and changed...
Replies
3
Views
635
Hi all, I'm in the UK and have recently had a ducted extractor fan Mixflo 200W with timer fitted. The fan comes on with the pull cord and runs for...
Replies
6
Views
321

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock