Good afternoon everyone.
I have fitted an extractor fan in my bathroom with an overrun timer, to start when the bathroom led lights are turned on. I have wired the feed to the fan via an adjustable overrun timer and DP isolator with the SL for the fan timer coming from the light switch.

The issue is with lights and fan off the LEDs are flickering dimly - this stops when the DP switch is opened. I assume there is a small leakage to N from somewhere in the timer causing the sensitive LEDs to flicker, which when the DP switch is opened cannot occur hence the flicker stops.

I have bought and fitted a 47nF 100r capacitor and connected it to all possible combos in the timer - no change. The only thing that stops it is if I disconnect the SL from light switch yo timer - but obviously the fan wont run now.
I have spoken to a qualified sparky who's only suggestion was the capacity action as a snubbed - he doesn't know what to do now!

I am stumped and would appreciate any advice please.
 
I don't remember a 12v driver/transformer in any of the other sketch's, is it supplying 12v to just that one bulb or all of them?
See post #33. Supplying just that bulb is my understanding. It was rather hidden amongst all the dialogue and explains why the halogen is not itself an adequate 'snubber'.
So I took the liberty of adding it to the diagram!!
 
I suspect that the electronic circuit in the manrose 1351 timer is acting as a dc voltage source circa 14V at its SL output. Tomorrow I will draw you a sketch of what I think the innards of the 1351 looks like. This small voltage current source is sufficient to light the low wattage LEDs dimly. Being dc the snubbers are ineffective since they are a series capacitor -resistor combo.

What we need is a voltage dependent way of isolating the SL output on the 1351 from the conductor going back to the SL on the connector strip to which the LEDs are connected. A zener diode is a possible way. Please would you obtain a few - say 5 to 10 - of these 24V Zener diodes. Here is a link to Rapid Electronics website but using the Amazon and search for 'BZX85C24' you will probably find some of them:

Vishay BZX85C24 24V 1.3W Zener Diode - https://www.rapidonline.com/vishay-bzx85c24-24v-1-3w-zener-diode-47-3088

When you have them you will use another connector strip to mount either one or two of these Zener diodes in series with the SL just as it connects to the SL terminal on the Manrose 1351 timer. I will show you how in a picture once you have the Zener diodes. The diodes need to be connected the right way round. For voltages less than 24 V they do not conduct but over 24V they become conducting. Thus they act like voltage controlled switches. Using one puts a block on V < 24V whereas two in series would block when V < 48V. Thus for V of 14V at SL on the 1351 the circuit path back to the LEDs is effectively open circuit so no current flows to illuminate the LEDs dimly. Well this is my analysis but the proof is by testing the scheme out.

Note well: Just because they are 25 V Zeners their leads are at mains voltage so they will need insulating and an enclosure.

See my sketch attached.
 

Attachments

  • IMG_1599.jpeg
    244.7 KB · Views: 15
Last edited:
I suspect that the electronic circuit in the manrose 1351 timer is acting as a dc voltage source circa 14V at its SL output. Tomorrow I will draw you a sketch of what I think the innards of the 1351 looks like. This small voltage current source is sufficient to light the low wattage LEDs dimly. Being dc the snubbers are ineffective since they are a series capcitor -resistor combo.

What we need is a voltage dependent way of isolating the SL output on the 1351 from the conductor going back to the SL on the connector strip to which the LEDs are connected. A zener diode is a possible way. Please would you obtain a few - say 5 to 10 - of these 24V Zener diodes. Here is a link to Rapid Electronics website but using the Amazon and search for 'BZX85C24' you will probably find some of them:

Vishay BZX85C24 24V 1.3W Zener Diode - https://www.rapidonline.com/vishay-bzx85c24-24v-1-3w-zener-diode-47-3088

When you have them you will another connector strip to mount either one or two of these Zener diodes in series with the SL just as it connectes to the SL terminal on the Manrose 1351 timer. I will show you how in a picture once you have the Zener diodes.

Note well: Just because they are 25 V Zeners their leads are at mains voltage so they will need insulating and and enclosure.

See my sketch attached.

Nice thinking. It will be interesting to see where this goes. Seems like it is definitely linked to the fan somehow.
 

I turned up this ‘open up’ of a manrose timer fan. If you look at 4m50s you will see the chap has sketched the timer circuit and shows how the SL input is connected to the circuit. Just by looking at the adjacent circuitry of diodes and r3istors and capacitors you can see the possibility of dc current flowing out of the SL terminal. Also the measured 14.1V at SL wrt to N is in accord with the Zener diode voltage rating of 14.7V. The SL input responds to the light switch closure during the negative half cycle of the mains voltage sinusoid.
An external Zener may work then if connected in the way I showed earlier. May need to trial a few blocking voltage levels though.
 
Nice thinking. It will be interesting to see where this goes. Seems like it is definitely linked to the fan somehow.
I think that's the problem, the OP's fan has its own timer originally he had both the Manrose unit and the timer on the fan operating, did advise him to disconnect the fan timer, but it may need to be by passed.
 

I turned up this ‘open up’ of a manrose timer fan.
Thank you so much Marconi for that.
Just a heads up that the OP has a separate run-on timer, which I think is the one below.
I believe he has connected the fan SL and L together at the fan, and then connected that combination to the Manrose 1351 unit. So I think what we are battling with is the SL of the Manrose 1351, which may or may not be a similar thing?
https://www.NoLinkingToThis/p/manrose-1351-remote-bathroom-fan-timer-control/83794?

I haven't yet found a circuit diagram for the 1351, only the usual installation bumf that is everywhere.
 
Last edited:
Hi Clanky
If you haven't given up already (and by the 70th post perfectly understandable) could you take a pic of the insides of the Manrose 1351 timer and post it here. I believe you bought a second one in case the first was faulty (which it wasn't)?
PS from the pic below, it may be slightly tricky to get into it - don't break anything, I'd rather you left it!

IMG_0239.jpeg
 
Last edited:
Hi Clanky
If you haven't given up already (and by the 70th post perfectly understandable) could you take a pic of the insides of the Manrose 1351 timer and post it here. I believe you bought a second one in case the first was faulty (which it wasn't)?
PS from the pic below, it may be slightly tricky to get into it - don't break anything, I'd rather you left it!

View attachment 110023
I'll try and open a spare tomorrow and get back to you, thanks, Mark.
 
Apologies Marconi - I read your post #66 before your earlier post 64 and was so absorbed I failed to realise in the latter you were talking about the Manrose remote 1351 timer, not the fan itself, so my subsequent post 69 was completely unnecessary.
Thank you again for your very useful input.
 
I drew the zener diodes connected the wrong way round in my first post. To block the +14V they need to be as in the sketch attached.
 

Attachments

  • IMG_1600.jpeg
    58.7 KB · Views: 14
Hi Clanky
Do take the advice of Mr Marconi, who is a very knowledgeable and well respected member of this forum, and buy the zener diodes he suggests (cheaper than snubbers if you find the right supplier).
All the evidence suggests this will solve the problem!
Avo Mk8 - i have taken Mr Marconi's advice and ordered Zener diodes - will fit them when they arrive.

Mr Marconi, thank you for the advice i have/will take it - zeners ordered.

Mike Johnson- for info 4 pmr209s fitted - I per led JB, still flashes like a hell until the fan stops then just very dimly.

Everyone - worthy of note: I think Mr Marconi may hold the answer because after the SL trigger signal has been sent to the timer from the light switch, and the lights are off but the fan is running on, if i then disconnect the SL at the 1351 timer all flickering stops - a Zener would do the same as my disconnection.

I really appreciate everyone fighting on with me on this - I don't like to be beaten and appreciate the help - I will keep all updated.
 
Hi
Apologies for chiming in on this.
It occurred to me if you are using the Manrose 1351 back box supplied with it, that's an enclosure that you could use right away!
Probably a good idea to sleeve the leads of the diode, though doesn't have to be heat-shrink!
You could put the banded end of the diode in the SL terminal of the Manrose, and stick a single choc block, or 2 hole Wago on the other end of the diode, and add the wire that was previously in the SL terminal.
Or a more elegant and robust method (for the diode) would be to put the diode across the terminals of a twin choc block, and then wire that to the SL terminal and the switch cable.
That all assumes there is enough room amongst the wiring already in there!IMG_0239.jpeg
 
Last edited:
Hi
Apologies for chiming in on this.
It occurred to me if you are using the Manrose 1351 back box supplied with it, that's an enclosure that you could use right away!
Probably a good idea to sleeve the leads of the diode, though doesn't have to be heat-shrink!
You could put the banded end of the diode in the SL terminal of the Manrose, and stick a single choc block, or 2 hole Wago on the other end of the diode, and add the wire that was previously in the SL terminal.
Or a more elegant and robust method (for the diode) would be to put the diode across the terminals of a twin choc block, and then wire that to the SL terminal and the switch cable.
That all assumes there is enough room amongst the wiring already in there!View attachment 110082
Thank you - I will try the double choc bloc option, I think there will be room. I wasn't sure if there would be any heat generated by the diode.

Many thanks Mark.
 
Clanky boy - good evening Sir.

I was pondering one of your earlier posts which included a wiring schematic. I have included it is an attachment below.

In my blue balloon marked X do you in reality have three wires going to the single pole light switch?

I have another very simple idea to solve the problem.

Others might like to ponder it.
 

Attachments

  • clankyboy.jpg
    363.6 KB · Views: 17
Last edited:
Clanky boy - good evening Sir.

I was pondering one of your earlier posts which included a wiring schematic. I have included it is an attachment below.

In my blue balloon marked X do you in reality have three wires going to the single pole light switch? I have another idea to solve the problem.

Others might like to describe it. There are at least two ways of doing it.
Not my post #60 by any chance?
 
The OP Was advised early on that the switched live from the Manrose is automatic and the cable from the switch was not necessary, the connection ought to be from the Manrose timer to the fan, but the fan also has an internal timer which to my mind makes confusion for the Manrose unit.
 
The OP Was advised early on that the switched live from the Manrose is automatic and the cable from the switch was not necessary, the connection ought to be from the Manrose timer to the fan, but the fan also has an internal timer which to my mind makes confusion for the Manrose unit.
Mike, i don't undestand the 'Manrose S/L is automatic' - it needs a S/L input to function, hence the connection from the light switch. The fan and built in timer are not confusing anything, as they are effectively 'dumb' with the built timer set to max run on of 30 mins, and the actual run on time being controlled by the Manrose 1351cutting the permanent live.

Nicebutdim - taking the S/L from the JB is essentially the same as taking it from the switch so would still allow a path for the V to the leds, sonkoving it wouldmake no difference I'm afraid.

Everyone - I think i have found the issue. The manrose timer has 146v on the S/L terminal after the light switch is off - this is feeding back via the S/L in the switch to the led lights.

All the other other manrose 1351 timers I have in place elsewhere and working (6 in total) are showing voltages between 96v and 135v. I intend to install a 200v zener diode in this circuit see if this solves it.

I'll let everyone know how I get on. Diode due here tomorrow.

Regards Mark.
 
Mike, i don't undestand the 'Manrose S/L is automatic' - it needs a S/L input to function, hence the connection from the light switch. The fan and built in timer are not confusing anything, as they are effectively 'dumb' with the built timer set to max run on of 30 mins, and the actual run on time being controlled by the Manrose 1351cutting the permanent live.

Nicebutdim - taking the S/L from the JB is essentially the same as taking it from the switch so would still allow a path for the V to the leds, sonkoving it wouldmake no difference I'm afraid.

Everyone - I think i have found the issue. The manrose timer has 146v on the S/L terminal after the light switch is off - this is feeding back via the S/L in the switch to the led lights.

All the other other manrose 1351 timers I have in place elsewhere and working (6 in total) are showing voltages between 96v and 135v. I intend to install a 200v zener diode in this circuit see if this solves it.

I'll let everyone know how I get on. Diode due here tomorrow.

Regards Mark.
The 146V doesn't really tie up with the previous measurement you mentioned. Is it ac or dc?
It sounds like the circuit in the 1351 is different from that in the fan run on timer (which is probably a good thing!)
If your other Manrose timers are giving a similar voltage, are they not in parallel with LED bulbs and making them flash?

At this point I'd go for the double pole light switch solution.
I know, I know, you've got a brushed platinum light switch plate and can't possibly change it!

I suspect a 200v zener might not provide enough of a step change to operate the timer, but worth a try I guess.
Sorry the efforts so far have not fixed it.
 
If zener does not work we can use current single pole switch plate to control a mains coil relay with double pole Normally Open contacts like this one:

Finder 66.82.8.230.0300 - 30A Flange Mount Power Relay 230VAC DPST-NO - https://www.rapidonline.com/finder-66-82-8-230-0300-30a-flange-mount-power-relay-230vac-dpst-no-49-3969
Mr Marconi, Avo mk8, Mike and everyone else - the 200v zener has sorted it - thank God.
I'm now off to have 10 pints!!!
On a serious note, thank you to everyone that have chipped in, added value, and acted as a sounding board - you have all worked through this with me, putting up with my rubbish diagrams.
Thank you all again, and hopefully i won't need to bother you guys again,
Kind regards,
Mark.
 
Mr Marconi, Avo mk8, Mike and everyone else - the 200v zener has sorted it - thank God.
I'm now off to have 10 pints!!!
On a serious note, thank you to everyone that have chipped in, added value, and acted as a sounding board - you have all worked through this with me, putting up with my rubbish diagrams.
Thank you all again, and hopefully i won't need to bother you guys again,
Kind regards,
Mark.

Have an extra pint for me. Glad you got it sorted. Just shows there are some clever people on here. And me of course :)
 

Reply to Flashing LEDs when fan and lights off in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock