Discuss flat submains and landlords suuply in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
4
hi ya'll

got a query, just questioning my judgemet

been o look at a job were a spark has done a disappearing act and work needs finishing the scenario-

total rewire, new3 phase mains incoming and gas etc

5 storey building
x4 new flats all new installs

by the entrance ground floor x4 submains each has 100a switch fuse cutouts for each flat and a landlords c/u. all fed via 25mm 3 core SWA from DNO 100a cutout in the basement.

my thinking is they should have switch fuses in the basement as its 20+ metres from DNO cutout to the switch fuses?

also the landlords supply has no switch fuse at all, just straight from DNO isolator.

the 2 mini boards are for pump for 2 of the flats

pic
 

Attachments

  • drapery board.jpg
    160.1 KB · Views: 137
I don't think its the fellas work if I'm right, but yea was thinking that, bit of sleeving.

Anyway those tails from the armoured will get snagged too.

I can't look at that pic any longer.
 
Thats right or M/C switch fuses bushed directly into the metal trunking eliminating the need for non sheathed armored cable cores
 
Alright I'll be a brave boy bloody awful rip it out and start again, complete crap
 
Hi,

I don't know where to start , there is so much wrong with it. As Pete says rip it out, start again and do it right. Trying to put right what is already there will take longer than re-doing the job.

Regards.
 
Trunking already in situ, M/C Switch fuses bushed into said trunking underneath, SWA terminated into said trunking, unsheathed SWA core run into individual Switch fuses with appropriate earth sleeveing . Insulated and sheathed tails run to DNOs equipment, all nice and neat and safe oodles of space left
 
y4ebype4.jpg
 
I think you've already stated your doing one but before I'd even consider touching this stuff it would be a day or two of indepth inspection/test (EICR) to baseline the whole installation --- if you think it looks bad at this end I be scared sh*tless would might have happened at the flat ends!. Then and only then can you discuss the way fwd with whoever owns the place and how you are going to rectify & certify it?!?!
 
yes I have commenced an EICR today and going through the 4flats ad found some issues that I have been asked to address as I go. only seen the basement today as couldn't access it on my initial visit, hence my concerns and sound advice needed
 
I'd be cautious just in case the previous guy bailed because of non payment.

Maybe just do the EICR and issue an invoice.
See how it goes from there.
 
I have been paid for today on the job, and I have done a different job for the contractor ordering the work and paid for that also, so im not worried on that front, in any case they wont get any paperwork until im fully paid
 
The sparks haven't followed recommended colours for multi core cables, ie where multicores are used, new colours
Brown live
Grey Neutral
Black Cpc
 
The sparks haven't followed recommended colours for multi core cables, ie where multicores are used, new colours
Brown live
Grey Neutral
Black Cpc

No right or wrong way, as long as the cores are identified at all terminations and the GY or bare copper CPC isnt used for anything other than earth or CPC
 

Reply to flat submains and landlords suuply in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
940
Afternoon All, Just pricing up a job and thought I'd pick your brains. Quick run-down, Block of Flats with an underground car park. In the...
Replies
27
Views
2K
I’ve got a job to quote for turning 1 big flat into 2 smaller flats. The DNO are looking at installing new meters in the communal area. I need to...
Replies
3
Views
1K
When doing an EIC for an additional circuit (which only covers that circuit), does the 'main switch/switch-fuse/circuit-breaker/RCD' section refer...
Replies
1
Views
1K
Hi everyone I've moved into a flat and I've decided to replace the original electric switches and sockets with white ones. I've done them all...
Replies
3
Views
913

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock