Discuss Flexible steel conduit as mechanical protection in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Reaction score
2
Hello I’m new to the forum (posting on it anyway). I could do with some advice...

Over the last 2 years I have been subcontracted (labour only) to commission solar PV systems. Often these are newbuild properties and when I get there the panels are already on and the DC cabling done.

About half the time the inverter is downstairs next to the CU and so the DC cabling is routed in the plasterboard stud walls in flexible steel conduit and clipped every 40 cm. In some places this cable run is within 50 mm of the surface of the finished wall.

The main contractor who is responsible for selecting and specifying this conduit was under the impression that it was sufficient mechanical protection as per reg 522.6.204 (iv) but I think this is wrong.

I have mocked up the situation and done my own rudimentary test. The conduit deflects away from a nail or screw in between clips, but if it happens where the clip is, or where the conduit is otherwise held, then on the nail or screw will easily pass through.

So my questions are -
What are the risks from the DC cabling?
What would happen if someone did put a screw or nail into one of the string cables?
What would happen if they hit both?
 
i would not consider flexible conduit to be suitable for that purpose.
 
I think the particular reg also says "although this may not be practically acheivable" i.e. steel covering will not effectively ensure protection. I think that is a fact in the real world. What I would say is, it is better than just the wire on it's own. If you find it is not adequate and does not meet regs, what will the remedy be according to regs. There is no such remedy in the regs so it is a difficult one to follow through on.
 
Thanks for the replies so far :)

I agree that it is not suitable James and Vortigern I think DC cabling hidden in the building fabric is best avoided ( ie should be run on the surface thus avoiding the issue altogether)

Does anyone have any knowledge as to the second part?

What would happen if one cable does get pierced by a nail, screw or drill?

What about if both do?
 
Thanks for the replies so far :)

I agree that it is not suitable James and Vortigern I think DC cabling hidden in the building fabric is best avoided ( ie should be run on the surface thus avoiding the issue altogether)

Does anyone have any knowledge as to the second part?

What would happen if one cable does get pierced by a nail, screw or drill?

What about if both do?
HI, I've attached a picture from the IET code of practice that best covers what you're asking. Simon
 

Attachments

  • 20211212_122817.jpg
    199.5 KB · Views: 18
  • 20211212_122823.jpg
    127.2 KB · Views: 18

Reply to Flexible steel conduit as mechanical protection in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hi, My first post so hopefully I am correct in posting it here. My question is, I am thinking of an IP rated outdoor socket for the back garden...
Replies
3
Views
1K
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
554
Hello, I am burying a fiber optic cable so I have internet in my garage. I have purchased the following flexible conduit to run the fiber optic...
Replies
2
Views
846
Hi, I'm a little confused confused is someone can shine some light on the amendment 2 way of doing IR. I know you have to do one 1st fix at 500V...
Replies
6
Views
2K
Is anyone aware of any galv trunking that is smaller than 50x50. I'm drawing a blank online. I've taken over a job that's used 16mm twin and earth...
Replies
12
Views
797

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock