Discuss Florescent Lights in the Australia area at ElectriciansForums.net

S

SKY

Hi All

Just purchased 4 36W single florescent lights from local merchants.

Why do they only have a 3 way connector block inside them, I need to loop them together so need a 4 way, there is no room in my fittings to put in a 4 way and utilise the earth tag on the fitting.

Are you allowed to have a floating connection inside the lamp fitting with the use if a single extra choc?

Thanks

SKY
 
bung a 2 wire wago in for your loop.it's enclosed in the fitting, so no problem.
 
The ones I get normally have a 4th block. Whenever there isn't I use a wago to loop. Seen plenty with a single choc wrapped in brown tape. Neater job with a wago IMHO.
 
I know thorn packs have 4 term but nothing wrong in creating another terminal, If you don't want it floating just replace the 3 block with a 4 block. I know what i would do though as there are other things to worry about other than a conection in an enclosed fitting.
 
you could install a junction box then screw it down inside the fitting, that way the connections could be made further from the lamps terminals and secured. if wanted an even cleaner look you could go to the effort of installing a junction box above the ceiling, that would make any future lighting installations a lot easier, 1 cable hanging out of the ceiling instead of 4 or 5
 
probably had to replace the fitting again.
 

Reply to Florescent Lights in the Australia area at ElectriciansForums.net

Similar Threads

Hi I've been planning to fit an outdoor junction box at the front of my house to hide a large brickwork hole and properly house the wiring...
Replies
9
Views
891
Hello, I'm replacing standard light switches in my hall and landing with touch switches (not smart, just touch on/off) like these from Amazon...
Replies
7
Views
621
I have a strip light in the kitchen operated from a single switch. I want to replace it with a straight bar 4 spot array. There are three supply...
Replies
2
Views
447
Hello, Looking for DIY electrical advice. I have 7 x spots, and each are fitted with 1 x T&E connector block fitting [see photo]. In the past...
Replies
3
Views
654
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
629

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock