Discuss fluke 1653b efli readings in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

stumas

-
Reaction score
1
ive just purchesed a new fluke 1653b multi tester when taking a eath fault loop reaqding on loop no trip setting i get a differant readng to when i take a reading on the hi current setting is this meter faulty
can anyone help the readings i get on the same 32a ring socket are

notrip setting 0.64

hi current setting 0.50

as you can see on the nontrip setting is higher and woulld fail as max is 0.58
 
Don't think you have a fault. I have done the same experiment with various meters and always get a higher reading when using the low current test.

It's because the no trip test uses a very short pulse and the RCD has significant inductance, so the observed figure is higher.
 

Reply to fluke 1653b efli readings in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all, This maybe a silly question and if it is please go easy lol!!!! I have a fluke 1653b MFT and am having trouble doing a Zs test on a...
Replies
13
Views
6K
I bought a brand new fluke 1653b just before Christmas, however I haven't really used it much as its mainly for personal use as I am looking to...
Replies
23
Views
7K
G
Hi, Just wondered if anybody could offer some guidance on a fluke 1653b tester. I was just wondering what the correct procedure is to...
Replies
1
Views
1K
44ALLAN
4
J
Guys (n' girls of course) I have just started using a 1653B FLUKE and when testing earth loop impedance Ze (ie. impedance of supply - tested at...
Replies
10
Views
26K
1shortcircuit
1
Has any used the Fluke 1653B yet? The all new Fluke 1654B multifunction tester is an excellent downloading tester, with time saving features...
Replies
9
Views
11K
Idris Benton
I

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock