Discuss fluorescent lighting installation in the Australia area at ElectriciansForums.net

Amp David

-
Mentor
Arms
Reaction score
904
Had a look at a job earlier which is to replace 9 6ft twin fluorescent fittings in a small warehouse.

At the moment there is nearly 20 single 5 ft fittings, all fed from 1 32 amp MCB:eek: and on 3 switches. All cabling is in 1.5mm t+e believe it or not:rolleyes: run on some cable ladder that runs the full length of the building.

My questions would be, Is it best or good practice to maybe split the switching of the 9 fittings into 3 lots of 3? As there is cable ladder installed, rather than installing conduit, then pulling in singles, would flex be an acceptable wiring method, cable tied to the ladder, then glanded into the light fittings?

If using HF fittings, will I still be required to use the 1.8 multiplier to do the calc for the circuit.

Thanks in advance:eek:
 
the 1.8 multiplier is to conpensate for the ballast so if using HF ballasts their is no need for it , is the supple single or three phase , if its three phase then i would split between phases , reason for this is the fact that there is a 50hz flicker on flourescents which in some circumstances can make moving machinary look stationary IE :lathes drills saws etc but buy using different phases this cancels out the flicker and i would do as you by splitting the lights into banks ,and as a good measure put some twin beam emergency lights in to with a test key at the switch bank ,cant see any reason why you cant use flex as long as its protected or not at risk of damage and current carrying capacity are within the requirements

Nick:rolleyes:
 
Cheers Nick.

See your point regarding HF fittings, so I can use the stated wattage to calc from?

Its single phase, but thought about splitting just for switching purposes, so they don't all have to be on together.
 
good idea to split them anyhow-for maintenance and simple avoidance of blackout,

as already said i don't think the 1.8 multiplier and 50hz flicker apply to hf ballasts
 
one 32amp mcb feeding 1.5mm? interesting. I would be spliting the lights and putting in an appropriate mcb.

Yeah, I found that bit interesting. Looks like the last guy just stuck in what he had. If all the fittings were actually working then i think he'd of had melted cables before now
 
have you seen the anti shatter covers for tubes that would be so good the amount ive broken in the van , i did notice the 1.5 on 32 amp mcb didnt need to mention it because im sure david being the proffesional he is will sort that out , i cant remember wether you said you were splitting the circuits to multiple MCB's or just switches would be a good idea on multi ple circuits then if you loose a circuit you dont loose everything ,

david , i did have a bizzar situation with HF and tubes and dave elec has said , i was in a church upgrading the lights it was cold in the - when we had the very cold spell before xmas we replaced all the 1060's ballasts for modern HF ballasts and when we powered them up they were pink and had a rolling sphear it was very wiard never seen it before but after about 10 mins it went to full brightness and has not given any problems since
 
You're right Nick about splitting over multiple MCBs, only problem is that customer won't want to fork out the extra on a bigger board. At present its a single phase sub board, 8 way and its full. Best part is that all circuits are protected by a 30ma RCD:confused:

My plan is to stick to what the customer asks for, provide him with quotes for his ideas and then mine and see what he does.

He's one of these guys who will only ever want the basic job done. For example his forklift charger keeps taking out the RCD on the same board. Advised on putting it on its own small CU, but wasn't interested. So instead he comes in every morning just hoping it didn't trip 10 minutes after locking up the night before:confused:
 
Just a note for those interestead in whats going on in the rest of EU By law we would have to split into 3 zones Probably 3 10A mcb's emergency lighting circuits on each of three zones then seperate switches on ech zone .....No more using mcb's as light switches . Just posting this as it may be of interest to some.
 
Would never even dream of use the MCB as a light switch anyhow.

Emergency lighting hasn't been mentioned, so will hopefully do this job, then when the H&S chaps pops back in and says wheres your emergency lighting, I might get the work!
 
Last edited:
not ideal really at all

fluorescents and sockets all on the 30mA

ther'd prob be some additional leakge if you use HF

you'd need the twin spots just for the nuisance trips alone- never mind blackout and local circuits tripping
 
not ideal really at all

fluorescents and sockets all on the 30mA

ther'd prob be some additional leakge if you use HF

you'd need the twin spots just for the nuisance trips alone- never mind blackout and local circuits tripping

One of my customers has a big industrial steel frabrication work shop one of four on site this work shop is full of welders HF flourescents ,drills , fork lift chargers ,and a massive sheet steel bending machine ,and a 30ma Main switch RCD which works perfectly it has tripped and does trip ,when there is a fault which with the nature of the work they carry out isnt suprising with hot wels burning cables and sharp metal edges that cables gets trapped on , tools are PAT testes every 3 months and at the same time the RCD's are tested and a visual carried out on sockets etc so may not nesseserily trip inconvieniently
 
One of my customers has a big industrial steel frabrication work shop one of four on site this work shop is full of welders HF flourescents ,drills , fork lift chargers ,and a massive sheet steel bending machine ,and a 30ma Main switch RCD which works perfectly it has tripped and does trip ,when there is a fault which with the nature of the work they carry out isnt suprising with hot wels burning cables and sharp metal edges that cables gets trapped on , tools are PAT testes every 3 months and at the same time the RCD's are tested and a visual carried out on sockets etc so may not nesseserily trip inconvieniently


scary :)-100amp 4-pole ya

and more 30ma's downstream
 

Reply to fluorescent lighting installation in the Australia area at ElectriciansForums.net

Similar Threads

Hello, I'm replacing standard light switches in my hall and landing with touch switches (not smart, just touch on/off) like these from Amazon...
Replies
7
Views
624
Hi, plumber here so please be gentle (or take the p-ss ;) ), I am supposed to be installing a UV water steriliser for a customer. I have some...
Replies
16
Views
2K
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
873
I live in a warehouse condo, converted about 20 years ago. The building dates to about 1870 but with the conversion, all of the electrical was...
Replies
3
Views
494
Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
632

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock