Hi

Reference Dead tests in 2392-10.In any of dead tests does functional earth lead on RCD. have to be disconnected as per RCBO,s??


I have surface mounted PVC light switches on upstairs circuit with open ended CPC,.s.Will this affect R1+R2 readings?? As they are a little high


Angus.................Still learning
 
Do RCDs have a functional earth lead? I haven't seen any.

If by open ended CPC you mean that it is not connected to an earth terminal in the light fitting, then this will not affect the R1+R2 readings as you will be testing from the end of that CPC.

High readings can often be caused by loose connections, just make sure the terminals are done up securely for each fitting and switch (and in the CU).
 
thanks for that .Have checked RCD( BS EN 61008).Definitely has white fly lead running to MET.The reason for the Question is that in Insulation Resistance Test they advise disconnection of functional earth on RCBO,s would this be the same for rcd fly lead.? RCD: MEM A100 HE

Angus
 
If there is a fly lead then yes I would disconnect it as it would be irrelevant to the testing of the fixed wiring, could cause a false reading and just in case it would fry the RCD!
Just my opinion not really backed up by proof, just same as you; sounds like a good idea.
 
Do RCDs have a functional earth lead? I haven't seen any.

If by open ended CPC you mean that it is not connected to an earth terminal in the light fitting, then this will not affect the R1+R2 readings as you will be testing from the end of that CPC.

High readings can often be caused by loose connections, just make sure the terminals are done up securely for each fitting and switch (and in the CU).
some of the MEMs had em richard....they use em on the big rig for the 2391 n all.....to see if candidates can recognise the presence of functional earths ......
 

Reply to Functional Earth on RCD in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
696
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
989
Hi Can anyone clear up or explain in a bit more detail what could potentially be causing the results I have. I have just tested a 32a ring main...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock