He may have legitimate reasons for suggesting a replacement.
Increase his income maybe?
Discuss Fuse Box/Fuse board - supply and fit in the The Welcome Forum area at ElectriciansForums.net
He may have legitimate reasons for suggesting a replacement.
He may indeed, but imo it's doubtful, no testing a quick look and oh yes madam you need a new fuse box that'll be£--- put your own figure on that Westy, you're a good bloke, but in this case far to trusting.He may have legitimate reasons for suggesting a replacement.
Yeah but easily rectified to a 30ma?It looks like a 100ma RCD though. And yeh...proteus.
Never spotted that, probably the reason then.It looks like a 100ma RCD though. And yeh...proteus.
Probably right Westy, but any self respecting Sparky would recommend an RCD change, wouldn't they???Never spotted that, probably the reason then.
I personally wouldn't go down that route and whilst you shouldn't base this on brand it would sway me. But as you say replacing the main rcd switch is of course possible.Probably right Westy, but any self respecting Sparky would recommend an RCD change, wouldn't they???
What would you do then Westy? change the CU without regards to any testing or inspection, cus all this Muppet has done is look at the CU and thought "hang on some easy money to be made here.I personally wouldn't go down that route and whilst you shouldn't base this on brand it would sway me. But as you say replacing the main rcd switch is of course possible.
How have you come to that conclusion. I can't find any post by the OP that suggests that?What would you do then Westy? change the CU without regards to any testing or inspection, cus all this Muppet has done is look at the CU and thought "hang on some easy money to be made here.
We don't know what the electrician has done.What would you do then Westy? change the CU without regards to any testing or inspection, cus all this Muppet has done is look at the CU and thought "hang on some easy money to be made here.
Probably right Westy, but any self respecting Sparky would recommend an RCD change, wouldn't they???
Why is that Steve? May be I'm a pessimist never trust anybody unless you know them and then think twiceProbably right Westy, but any self respecting Sparky would recommend an RCD change, wouldn't they???
From the image the unit looks a little aged, with all the testing we can do with a MFT on the circuits, we still can't test the existing mcb's.
Even if the RCD is replaced the CU would still have only one rcd for all circuits.
As already said, a decision shouldn't be made on the make, albeit my first comment was meant to be a comical one, the price I'm getting on my CEF web account is £52.52 for a replacement 80 Amp 30mA RCD.
To be fair, we've had no technical info or prices given, if the electrician can do a good deal it maybe wouldn't be such a bad call to consider an up-to-date twin RCD or RCBO CU.
Looks like we have a differing of opinions on this post, but I have said my bit.From the image the unit looks a little aged, with all the testing we can do with a MFT on the circuits, we still can't test the existing mcb's.
Even if the RCD is replaced the CU would still have only one rcd for all circuits.
As already said, a decision shouldn't be made on the make, albeit my first comment was meant to be a comical one, the price I'm getting on my CEF web account is £52.52 for a replacement 80 Amp 30mA RCD.
To be fair, we've had no technical info or prices given, if the electrician can do a good deal it maybe wouldn't be such a bad call to consider an up-to-date twin RCD or RCBO CU.