Discuss Generator Supply in the Canada area at ElectriciansForums.net

W

welshmadness

Hi all.
Going to be doing a standby generator installation soon and i need to work out a minimum duct diameter for the cables i intend to use.
The generator has a 630Amp merlin Gerin MCCB, i was going to use 2*300mm 4core s.w.a. cables, until i went and paid a visit to have a look at the generator, and was amazed at how little cable, glanding and termination space there was. So we done some re-calcs and now decided to use unarmoured singles (2*185mm tri-rated per phase)
Now, ive worked out that there will be 8*185mm and one 240mm earth cable going through this duct, each 185mm cable has a diameter of 32mm, and the 240mm had a diameter of 40mm.
Can anyone help? Been looking through the regs but cant find anything specific for what im trying to achieve :confused:

Thanks
 
Hi there.

Tri rated singles, deffo the best way to go. Done loads of geney systems upto 1MW and always used them.

What are you supplying/how far. Any risk of damage??

As for the duct I'm guessing your going underground??? if so just use the biggest you can get in there, makes life so much easier when drawing through.
 
Must be bigger than 150kva surely? wouldnt that only require the cable to carry 210ish amps per phase.

You could get away with 120mm 4core SWA in a duct:)

Then again im a duffer so i prob got it wrong lol
 
Yeah, sorry it is bigger than 150Kva, its a 410Kva.
Lenny, we are supplying a MCC for a pumping station, cable run is about 25meters, the duct (stainless steel) will run from the generator, through a concrete plinth and into a sub-basement where the singles will jump onto some ladder racking then into a mains/generator auto changeover unit.
The duct will be earthed as i see it as being an exposed conductive part.
There wont be much chance of damage to the cables as they will be mechanically enclosed, Generator vibration wont be a major issue.

I am thinking of a minimum 16inch diameter duct, not done one of these before so im a bit worried incase i spec the wrong size.

Thanks for the replies so far guys.
 
Hi there, thought that seemed small :)

AFAIK there is no regs (17th) with regard to space factor but after reading around apparently 15th edition quoted 45% which is what i'd go with as a minimum if I were in your position.

Just some scribbles but........

32mm diameter x 0.5, squared and multiplyed by pi = approx 804mm(squared) csa

40mm diameter x 0.5, squared and multiplyed by pi = approx 1256mm(squared) csa

8 x 804 = 6432 + 1256 = 7688mm(squared)

7688 / pi = approx 2447, sqrt of that is near as damn it 50, multiply this by 2 to give total diameter (of cables and insulation) = 100mm I would multiply this by 2 to allow for the gaps between each cable and then multiply this by 2.2 to allow space factor so this gives

440 mm diameter which is 17.3"

Whatdya reckon? I have no idea if this is ok BTW
 
Last edited by a moderator:
Just be cautious if paralleling your cables up when it comes to glanding them especially for a genie this size you need to avoid eddie currents forming within the gland plates usually achieved with used of a non ferrous metal or non metallic gland plate, depending on the load characteristics of the load; overheating, arcing, induced noise, rf issues etc are all major problems if done incorrectly. Appologies if im teaching you to suck eggs just gave impression you havent done this type of system before.
 
Thanks Montybaber.
I wasnt far off with my guesstimation of 16inch diameter, but was good to see some calcs from someone else.
I never did the 15th as i was still in school at the time so wasnt sure, so cheers for looking.
I plan using a 12mm thick pvc board from RS to be a substitute gland plate to eliminate eddy currents. Done a few genny sets before, but were only small 100A backup sets, most of which you could terminate S.W.A. into without much hastle..........until now lol.

I would post pics of the geny set on here, but no idea how as im still a virgin forum user

Thanks again for your replies.
 
You would have to host your pics on photobucket or the like... its really easy even I can do it lol

Just join photobucket, upload the pic and then copy the img text and paste it onto here and it appears :)

ps I dont remember 15th either lol im 29
 
IMG00027-20090612-1033.jpg


IMG00028-20090612-1033.jpg


well, gonna give posting a pic a go :cool:
 
that gland box is going to have a new home in the bin, going to manfacture a larger gland box where the singles will come in through the rear and hopefully have enough of a bend radius before connecting onto the mccb. its a lot of arsing about i must admit, hopefully the next ones the geny manufacturer will leave enough room for cables.
Can you imagine trying to make off 2*300mm s.w.a. in that enclosure:eek:...stuff that.
 
Might be worth a call to the manufacturer, it's possible they might pick up the tab for any mods if they accept that their kit is not fit for purpose.
Worth a try, unless your customer doesn't care about any additional cost.
 

Reply to Generator Supply in the Canada area at ElectriciansForums.net

Similar Threads

Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
840
When putting in some duct for fibre broadband we also put in a few lengths of 63/50mm twinwall duct "just in case" we needed that, as we knew of a...
Replies
9
Views
1K
Before I pay an electrician to come check my work, I thought it worth a post here. I don't want to pay the cost of a small car for a whole-house...
Replies
0
Views
1K
Hopefully someone wiser than me can help explain some odd measurements I’ve taken at my own home. This is a long read, I’ve tried to give as much...
Replies
21
Views
4K
I know how I was taught to test a RCD, 6 tests in all two no go, two under 300 mS and 2 under 40 mS with no load. But thinking about it not so...
Replies
7
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock