Hello all...

I am about to visit a property that has night storage heaters in it. The customer states they have one heater that is not working and they want it replaced. I have said that it may be fixable but they want a new one.

I have not installed any storage heaters before and wondered if you guys had any particular heaters (that store heat) that you would recommend as there are quite a few that states they are the best? It will need to be a storage heater as it is on a seperate CU on economy 7.

Cheers chaps.

ps.. Continuing to look for new avatar.
pps.. decided against the former picture Richard but thanks for sending :smile5:
 
Last edited:
Try the internal thermal reset and test the elements before replacement. They are not cheap to replace as a whole unit, although Dimplex would be my brand of choice.
 
How many elements are there? I would be surprised if more than 1 had failed at the same time!

Pay close attention to the incoming terminals - seen many which have over heated, and failed.
 
Try the internal thermal reset and test the elements before replacement. They are not cheap to replace as a whole unit, although Dimplex would be my brand of choice.

Thanks Andy,

If it is just the input cutout then I'll reset, also I'll have a quick test of the thermal fuse link.



How many elements are there? I would be surprised if more than 1 had failed at the same time!

Pay close attention to the incoming terminals - seen many which have over heated, and failed.

Not sure how many elements Murdoch, at least 3 probably 4 as it's large, so I doubt its the elements. I will check the terminals though.

Would anyone be able to explain where the input charge control thermostat is likely to be and how to test if that is faulty as if the other bits check out fine then this may be the problem?
 
The input charge controller is basically a set of points along with a reset usually ,on auto models theres also a capillary stat linked into it and that sits at the rear down the bottom , so depends what type and how old the model is , if you post a picture I can tell you what part you want from spares direct , you want to ascertain what the model is and if its Dimplex there will be a set of numbers on the top left hand side .
What you need to do is take a continuity reading at the input with the DP switch in the off position if its a 4 element model you should get around 18 to 19 ohms if you get not continuity you can simply follow the live up to the input controller and check each side of the contacts with the input turned up high, chances are its the input controller and thats quite common and I have replaced loads of them , if its an element there would have been some heat coming out of the heater..

If they want to replace the heater there is a table to work out the sizing of the heater on the dimples website , I would use that rather than going on the size of the heater as you should ensure the heater is properly sized for the room , Dimplex is you're best bet though although slightly cheaper versions made by dimples under other names are available make sure its an auto model you install though i.e. XLSN not the XLS, the 3 models are XLS12N , XLS18N, XLS24N , ( 2 , 3 or 4 elements)
 
Last edited by a moderator:
Some older models also have a thermal fuse Link..

And the major reason they go is either theres lads of dust and muck in the heater or people putting clothes over the heater, that can either be the rest type or a link that needs replacing , again can be checked when doing the continuity test ....
 
Last edited by a moderator:
Its funny how pub members get all the help they need but if an outsider asks the same question all he gets is are you qualifed or get qualified electrician or similar. Double standards, just saying. Btw not having a dig a op.
 
Its funny how pub members get all the help they need but if an outsider asks the same question all he gets is are you qualifed or get qualified electrician or similar. Double standards, just saying. Btw not having a dig a op.

Hum.... not sure about that.

The OP has a good track record of posting questions, offering possible answers, ANSWERING questions and giving thanks for input. Lots of people fail on almost ALL these points.
 
Its funny how pub members get all the help they need but if an outsider asks the same question all he gets is are you qualifed or get qualified electrician or similar. Double standards, just saying. Btw not having a dig a op.


Depending on who you are , you don't always get thanked for help either , I am fast coming to the conclusion of why should I bother anymore It's a nice little club on here, oh what the hell I can't be bothered anymore Goodbye
 
Depending on the circumstances and the availabilitly of a suitable 24 hour supply nearby I would be recommending fitting a Quantum. (Although it would be more expensive to buy out right than the equivalent normal storage heater). They are more economical and generally nicer to look at.
 
Last edited:
Its funny how pub members get all the help they need but if an outsider asks the same question all he gets is are you qualifed or get qualified electrician or similar. Double standards, just saying. Btw not having a dig a op.

Personally I tend to answer the question on its individual merits, not even noticing the name of the OP most of the time. Sensible questions get sensible answers, other questions don't
The only exception being the trainee section where every question gets a sensible newer from me.
 
Hello all...

I am about to visit a property that has night storage heaters in it. The customer states they have one heater that is not working and they want it replaced. I have said that it may be fixable but they want a new one.

I have not installed any storage heaters before and wondered if you guys had any particular heaters (that store heat) that you would recommend as there are quite a few that states they are the best? It will need to be a storage heater as it is on a seperate CU on economy 7.

Cheers chaps.

ps.. Continuing to look for new avatar.
pps.. decided against the former picture Richard but thanks for sending :smile5:

Storage heaters haven't changed in many many years, you'd almost certainly be fitting an identical unit to the one you remove. The circuit is very very simple and you should be able to work it out by tracing the wiring, also a Google search will turn up diagrams and pictures of spare parts which will guide you.

You'll need a Hoover to clean the fluff and crap out of it whilst youv got the lid off.
If you have to work on one which does work then get them to switch it off the day before otherwise it'll be too hot to touch inside.

If it's a dimplex one the screws you need to remove to get the cover off are on the bottom of the unit, one either side with a hexagon head (10mm I think) that you'll want a spanner for then the cover pulls forwards at the bottom and lift off. (I mention this as it took me far too long to work it out once)
 
I'd also check the connections and condition of the DP switch as I've seen them overheat and burn out quite a few times. Generally you'd get the pungent 'fishy' smell with that problem though.
 
Its funny how pub members get all the help they need but if an outsider asks the same question all he gets is are you qualifed or get qualified electrician or similar. Double standards, just saying. Btw not having a dig a op.
Not really "funny" - a pub member is likely to have become a pub member because they have made valuable contributions to the forum, and logically deserve help in return. They're also more likely to accept help instead of accusing everyone of elitism or snobbery or whatever, and less likely to ask a question then disappear never to be seen again after several members have put themselves out to suggest solutions.

If you think 'outsiders' should be getting more help there's nothing stopping you from helping them, and nothing to say that helping them has to be someone else's responsibility.
 
I would second dimplex quantum. Nice looking heaters, most of the rest look to industrial in my view. There are two slightly differing designs of them. But as Resu I think said they do require a permanent as well as off peak supply as they have a boost element and fan which may be needed come 10pm at night when the bricks start to cool.

HHD, there was a link on this website about models of NSHs that contain asbestos, worth looking at before dismantling any old models. Wasn't from that long ago.

Avatar for you:

https://lh4.googleusercontent.com/-...AAAAAAAAB8/2Vbob8Sbl60/s1600/NEW+HHC+logo.jpg
 
Last edited:
I would second dimplex quantum. Nice looking heaters, most of the rest look to industrial in my view. There are two slightly differing designs of them. But as Resu I think said they do require a permanent as well as off peak supply as they have a boost element and fan which may be needed come 10pm at night when the bricks start to cool.

HHD, there was a link on this website about models of NSHs that contain asbestos, worth looking at before dismantling any old models. Wasn't from that long ago.

Avatar for you:

https://lh4.googleusercontent.com/-...AAAAAAAAB8/2Vbob8Sbl60/s1600/NEW+HHC+logo.jpg

Thanks GO, I have a print out at home ready to take with me of all the models that contain asbestos. I had a very brief look at it whilst I was doing another job there and could not see a identification/model number or a make, it may be behind the casing though.
 
I did think of the Quantum and may well give that as an option to the customer, but if it needs a permanent supply as well thats going to bump up the cost so I suspect they will decline!
 
Yeah they are for the boost side of it there a lot bloody heavier as well think just the heater it self was 43kg I'm sure the older ones use to be lighter then that

Its not just the boost. If my memory serves me correctly they don't work without the 24/7 supply
 
If installing quantum heaters make sure the 24 hour supply is on something like thtc tariff .
i had to sort out a job where the installer had just plugged them into 13a sockets.
the woman's bill for a quarter was about £1000 .
the boost element switches on and off depending on what the room target set point is set to ,to keep the room at a more even temp than standard storage heaters
 
I would also recommend the dimplex quantum. Looked alright wasn't to much of a hassle to fit either. Even customer said they looked better then the old style heaters

Was easy enough to fit, only thing I didn't like was putting in the top row of bricks as you have to edge them over the element and it is a bit of a tight fit. Probably quite easy to damage the top element in that respect.

They have a lot of electronics going on in them as well for a NSH I thought.

DCF, the boost can obviously be turned off whilst keeping the stat temp as high as you like. But interesting to know about the thtc tariff. Will look into that.
 
Last edited:
Just got back from the job...

The problem turned out to be a broken neutral connection in the FCU by the side of the storage heater, it was well hidden though as the conductor went fully into the terminal but wasn't making any contact!

The lady did have a problem with another one of the the storage heaters too. It was occasionally tripping the MCB overnight.

It is a 2.55kW heater on a 10A breaker fed with a 1.5mm cable. It has a 13A FCU. In theory it should only be pulling around 11A so shouldn't ever trip the MCB. However this may be the problem and I wanted to hear peoples views on putting a 1.5mm conductor in a 16A MCB? I 'think' this is against the regs, but the 1.5mm cable is ref method C so the CCC is 16A, in addition it has a 13A FCU AND also reg 433.3.1 (ii) negates the need for overcurrent protection if the conductor is unlikely to carry over current due to the characteristics of the load (i.e 2.55kW = 11A).

Plus.. just checking appendix 15 and Fig15B actually shows a 20A MCB, so perhaps it isn't breaking the regs. I've just always put 2.5mm in a 16A MCB!
 
Just got back from the job...

The problem turned out to be a broken neutral connection in the FCU by the side of the storage heater, it was well hidden though as the conductor went fully into the terminal but wasn't making any contact!

The lady did have a problem with another one of the the storage heaters too. It was occasionally tripping the MCB overnight.

It is a 2.55kW heater on a 10A breaker fed with a 1.5mm cable. It has a 13A FCU. In theory it should only be pulling around 11A so shouldn't ever trip the MCB. However this may be the problem and I wanted to hear peoples views on putting a 1.5mm conductor in a 16A MCB? I 'think' this is against the regs, but the 1.5mm cable is ref method C so the CCC is 16A, in addition it has a 13A FCU AND also reg 433.3.1 (ii) negates the need for overcurrent protection if the conductor is unlikely to carry over current due to the characteristics of the load (i.e 2.55kW = 11A).

Plus.. just checking appendix 15 and Fig15B actually shows a 20A MCB, so perhaps it isn't breaking the regs. I've just always put 2.5mm in a 16A MCB!
is it only the one heater on it?

if yes then its a fixed load and i think you can as the load is on a 13amp fuse at max.

the cable has short circuit protection from the mcb and overload protection from the device
 
As long as its not in thermal insulation and VD is OK you can get away with a 1.5mm on a 16amp , I have come across 16amp mcbs on 1.5mm cable quite a though times in commercial environments.
 

Reply to Good replacement for a night storage heater? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I have an Economy 7 storage heater Dimplex CXL24N - 3.4kW Storage Heater + Convector ( there not available anymore) that dos'nt work and...
Replies
1
Views
614
Been round to a house to quote to replace some storage heaters for new panel heaters and came across a strange (to me at least) way of wiring the...
Replies
23
Views
4K
I get asked quite a lot about replacing old storage heaters with something more economical and I don't know what to recommend. Some people ask for...
Replies
9
Views
2K
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
217
Hi, So I'm trying to understand what's going on with my off-peak electricity supply, as something's wrong with it and I'm trying to determine if...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock