Discuss Grid switches for kitchen appliances in the UK Electrical Forum area at ElectriciansForums.net

B

Brianinlondon

In various forums I've seen it said that multiple kitchen appliances can be controlled via (unfused) grid switches located above the worktop, the grid switches being wired directly into the kitchen ring and leading to unswitched sockets where the appliance is appropriately fused.
Is this OK or would each circuit be considered a separate unfused spur? The ring is protected by a 30mA RCD.
Thanks for your views.
 
Well 30mA won't hold to much, what size is the cb? out of interest should be 32 A
 
depending on the load of the appliances, it's sometimes advantageous to install a 4mm radial dedicated to the appliances. feed to the grid switches in 4mm, then 2.5mm to each appliance.
 
the theory is that the plug fuse would protect the 2.5mm cable from overload, whereas the 30A in the DB gives short circuit protection
 
In various forums I've seen it said that multiple kitchen appliances can be controlled via (unfused) grid switches located above the worktop, the grid switches being wired directly into the kitchen ring and leading to unswitched sockets where the appliance is appropriately fused.
Is this OK or would each circuit be considered a separate unfused spur? The ring is protected by a 30mA RCD.
Thanks for your views.

A common misconception is that the BS fuse in plug tops and FCU's are there to protect appliances, they are NOT!! The function of these HRC fuses are to protect the leads and cords of the connected appliances etc. If an appliance needs overload protection, then it should be provided by the manufacturer, not by an external replaceable cartridge fuse, of various ratings....
 
in theory its nothing different to a couple of spurs taken off a ring. nothing wrong when some common sense has been used.
 

Reply to Grid switches for kitchen appliances in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello everyone, I'd like to seek your input on a matter. I'm in the process of designing the electrical connections for the following kitchen...
Replies
38
Views
3K
Currently planning a new rewire for my kitchen and want to get things right first time when it comes to appliances consumptions and circuits...
Replies
0
Views
986
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
870
Hello Electrical world. Looking for thoughts and opinions. Currently planning out my kitchen re-wire for new kitchen. I was originally...
Replies
13
Views
3K
Hi everybody, Looking at putting a kitchen grid switch in my kitchen and wanted to see what you guys (and girls) thoughts were about my set up as...
Replies
9
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock