Discuss H07RN-F FLEX MAINS suitability in the UK Electrical Forum area at ElectriciansForums.net

Midwest

-
Esteemed
Arms
Reaction score
10,616
At work in our main kitchen, the 6kW (26A sp) water packed up. The restaurant staff were in turmoil, as they had no hot water to make the tea. Luckily we had a new spare one lying around.

The old one was fed by a 32A supply, 4mm 6242B (LSOH) cable 32A RCBO. From the rotary isolator, the appliance was fed by a 3 core 4mm H07RN-F cable (about 1m). So I was just going to disconnect that from the old appliance, and reconnect to the new one.

However, once I disconnected it, I found the insulation on the cores had failed, it was crumbling away in places. The sheath was fine. The stranded conductors were slightly rigid. As the flex was too short to cut back, we got a new piece. No ferrules had been used on the terminations, but there was no sign of thermal damage on the terminals.

When I removed the old flex, it was pretty much the same throughout its length. No obvious sign of similar damage to the 6242B cable. I see that the 4mm H07RN-F cable is rated at 30-34A, depending on manufacturers.

So I can’t see the flex is being overloaded, terminals could of been a bit tighter.

No pic of cable I’m afraid. Thoughts?
 
Any idea how old it was?

Typical lifetime for cables is 25 years at max running temp, which could be the case here. But it might just have been a poor batch, or maybe the environment was rather hot so cable really running above its specification. Typically for chemical degradation effects lifetime is halved for every 10-20C increase in temperature, so maybe not burning but could have its lifetime brought down to a decade or so.
 
Found the old cable, pics.
D9F36D27-0824-43B8-8EC0-72C1CDB5A4C9.jpeg
89B6FC29-5D9B-4006-B319-2019D66BBFC5.jpeg
 
That doesn’t look like H07 to me.
Its marked as Vede H07RN.

The shorter stripped end was terminated in a junction box (in 15A strip connector!) and the longer end was terminated in the appliance. These longer stripped core's, were me pulling off the outer sheathing, before I realised the cable had had it.

The cable is not very flexible!

Started to have a look at the other appliances in the kitchen, seems to be the same sort of cable. None seem to have the same rigidity as this damaged cable, but I think further inspection is needed. I think if they are same source of cable, they might need replacing. We've got fryers, steam ovens etc.
 
Last edited:

Reply to H07RN-F FLEX MAINS suitability in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Ok i may get slated for this one but here goes; A bit of background info first. Its been a while since ive looked at my iee regs, and ive not...
Replies
12
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Came into work today with a fairly urgent requirement to install an instant hot water handwash unit in a small commercial kitchenette/servery -...
Replies
19
Views
2K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
768
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
839

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock