Discuss Had a weird CPC reading today in the UK Electrical Forum area at ElectriciansForums.net

Raptor0014

Esteemed
Reaction score
1,261
Doing an EICR today and had an odd, lower than expected, resistance reading on a ring final CPC.

r1 = 0.21Ω
rn = 0.21Ω
r2 = 0.18Ω
R1+R2 = 0.09Ω

I was expecting around the 0.35Ω for the CPC but was quite surprised to see the reading I got.

As this was the supply to a kitchen ring I could see and access all 7 2g sockets (property is empty but tenants were moving in later today) and the 2 switched fused spurs for the washing machine and under counter fridge. So I took all the fronts off and checked all terminations were correct.

The only thing I can surmise is that there is a parallel earth path somewhere on the circuit, but I couldn't see where. Nothing was ran in any conduit that I could see and all the cable entry points had normal grommets. I noted it in the comments section of the report anyway for future reference.

But wondered if anyone else had ever had that happen before? I never have and rang my CPS technical helpline to check and they agreed it is most likely a parallel earth path somewhere. Unless some of you more knowledgeable lot have any other suggestions?
 

Reply to Had a weird CPC reading today in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
1K
Hi Can anyone clear up or explain in a bit more detail what could potentially be causing the results I have. I have just tested a 32a ring main...
Replies
7
Views
1K
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
730

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock