mint2016

Hi. Im hoping someone may be able to offer some ideas on the above, as I've run out!

A 4 burner gas hob will not spark if plugged directly into the wall socket, bit if I route it via a 30m extension cable into the same wall socket it works a treat!

The instructions say the hob should be hardwired, but I have had a electrician say that this should not make a difference, and it should still spark with a plug fitted.... which it does, but only via the 30m cable!! The socket has been tested with no faults..

Has anyone ever heard of a situation like this as I am keen not to install the kitchen with a 30m cable stuffed down the back of the base units :-/

Regards,

Ches
 
Bit of a long shot but I have noticed before that the plug pins are sometimes shorter on some plugs. Normally not a problem but if the socket has blades a bit further back may not make contact.
Plug on ext lead may have slightly longer pins getting good contact.
Like I said long shot...
 
Bit of a long shot but I have noticed before that the plug pins are sometimes shorter on some plugs. Normally not a problem but if the socket has blades a bit further back may not make contact.
Plug on ext lead may have slightly longer pins getting good contact.
Like I said long shot...
 
Thanks.. I thought it maybe something to do with the actual plug also, so took the one from the extension and put it on the hob.. still no joy. I have now tried taking various plugs from other appliances and trying them, still with no effect unless the extension is used between hob and wall. Very strange.

Im now thinking that it must be something to do with the additional resistance from the extra cable, but I have no idea why it should work with increased resistance (and therefore a lower voltage supplied to hob?). I'm leaning towards a fault with the actual hob now..

Thanks again for the idea though..
 
Hi Mint - for my sins I've had to fix a few non sparking cooktops, but yours is a new one to me. I don't think the sparker is clever enough to know about cable impedance of an Ohm or two, so I reckon you are having a continuity problem. Perhaps bypass the spark switch so it sparks continuously while on the extension lead and see if that helps you find it.
 
What's the voltage going into the hob when plugged in direct and via the 30m extension?
Its possible the volt drop down the extension is allowing the hob to work. Which would indicate a fault with the sparker when presented with the higher correct voltage.
 
Hum.... what was the voltage at the "hob" socket? what was the Zs? and what happens if you plug something else into the hob socket?
 

Reply to Head scratcher with gas hob - will only spark when routed via a long extension cable. in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hi, Just looking for a bit of advice here. I am considering swapping my existing 4 burner gas hob for a Bosch induction one. I am not proposing...
Replies
10
Views
5K
One of the oddest jobs I've ever had today. Called by a plumber I know who had attended after a leak through the kitchen ceiling from bathroom...
Replies
24
Views
6K
Hi, We have a ten year old fridge-freezer plugged into an older socket (20 yrs plus I should think). It started tripping the RCD on the consumer...
Replies
7
Views
5K
Hi, I would appreciate some views on the following issue I have. The Cooker radial in a house has been wired in 2.5mm T&E, to save the expense...
Replies
12
Views
3K
R
Hi all. This is my first post for advice, so please take it easy on me. I am a recently qualified electrician on a completely new career change...
Replies
50
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock