Discuss Head Scratching time lighting fault in the Australia area at ElectriciansForums.net

Reaction score
1
Been doing an eicr today, went to do an R1+R2 on a lighting circuit and got no reading between earth and live but neutral to earth was 1.36 ohms. Straight away thought reversed polarity, but the luminair was working correctly before we arrived, so i put the power back on and checked the voltage at the fitting neutral to earth 0v live to earth 234 live to neutral 235v. everything there seemed to be right zs was 1.48ohms and ze was 0.11ohms. So everything added up how you would expect.

checked the r1 and r2 again encase i was doing something stupid same again 1.36ohms went back to the 1st light on the circuit as i had that down anyway and got an r1 and r2 (live to earth ) at .18 then at roughly the mid point the reading again was how you'd expect it to be 0.58 to live an earth.

any ideas? old building 30 years + old
 
You did have the light switch on for the R1 + R2 test?

You do know theres a case for not doing a R1 + R2 test on an EICR. If you look at the example in the OSG they have just put a tick in the R1 + R2 box, implying its OK because the Zs test was OK.
 
When verifying voltage at the light fitting, how did you connect your test leads? Did you put them directly on to L, N, E terminals at the rose/connector or did you use a plug-in connector for your L and N leads? If the latter, it is very easy to get polarity of test leads reversed.
 
i tested with my voltage indicators, and the fact the light fitting works normally suggest the correct polarity is there when live, 3 of us where there on site and couldn't work out what was going on. To be fair the place is a mess and needs ripping out and starting from scratch, but i'm interested in knowing whats going on here.
 
could it be possible that you got the no reading L-E with the switch off, and the N-E reading you got was a parallel path?
 
If you removed the live and cpc on the first run, you may have pulled the wrong cpc from the earthing terminal bar, but since you did it the second time and got an acceptable reading then all is now well?

The easiest way of achieving an R1+R2 result is to leave the cpc in the earthing terminal bar and connect the live to that bar
 
I switched the switch in all possible positions its a 2 way switch and still got no reading its really baffled us to what going on, other parts of the building has had many faults with shared neutrals, this board is the 1st time its been tested since 1983. And very little maintenance has been done in that time. all the neutrals go to the switches, but on one of the switches it has 2 different ciruits in in ones on red phase and the others on yellow it has 3 neutrals in it, but were' 99% certain we know what they're for and are nothing to with the circuit with this issue.
 
A classical guitarist mate, so "finger-picky" really :tongue3:

Also an HNC qualified electrical engineer with over 20 years experience, not that that has anything to do with the English language...
 
it is a tncs system i allways test when i can taking the neutral off the the board and the live and if its possible to identify the earth i will take that off but in this board i left all the earths as they were
 
Maybe a borrowed neutral on one end of the 2 way system that was still connected and extended the path being tested all the way back to the E-N connection at the supply point.
 
A classical guitarist mate, so "finger-picky" really :tongue3:

Also an HNC qualified electrical engineer with over 20 years experience, not that that has anything to do with the English language...

That's a bit 'irrelevant' when it comes to head scratching
 
Also an HNC qualified electrical engineer with over 20 years experience, not that that has anything to do with the English language...

similar to me then, except i can't play a guitar to save my life, nor any other musical instrument, but i can fart in tune.
 

Reply to Head Scratching time lighting fault in the Australia area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
395
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
I have just been in the process of changing some old 12v halogen downlights in the bathroom for bathroom for mains volt leds. My late father was...
Replies
2
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock