Hi all

I was wondering - do you think it's worth re-wiring the CylStat, so it's on ALL the time, as suggested by it's manual? (and what would I need to do, to achieve this?)

At the moment it only switches on when switching on the hot water..


See below revised wiring box
PXL_20220802_205109507.NIGHT_Original.jpg


Many thanks!
D
 
The green/yellow is the switched live from the stat, ideally that would fed the common of the thermostat which is currently done using the blue link wire within the stat. The brown conductor to the stat could the be moved to the permanent live terminal. You would need replace the flex for a 5 core as using the earth would be naughty...
 
To be honest, the cylinder stat was just the tip of the iceberg - just trying to solve things step by step.. 🤷‍♀️

My real problem is that my boiler seems to be overheating constantly, even though both heating and hot water are off.

After some discussions with the (somewhat questionable?) professionals mentioned previously, my understanding is that the following is happening:

The overheating causes the boiler pump to run almost constantly, as it tries to cool itself down.
(Observing it, I don't think it's actually firing up, but I could be wrong.)

While doing so it tries to pump water into the system. But with both HW and heating valves off, there's nowhere to pump to, so the pressure rises, and it get's stuck into a loop of doing the same over and over again.
This I can only assume is torturing the pump.


Seeing that the wiring has been rather sloppy, I'm suspecting that it might be a wiring mistake or the Nest that's causing the whole issue.

What do you guys think? 🤔


Photos of the current wiring box are just above and the Nest wiring, too.

Please let me know if you need further info, images or anything else for that matter..

MANY THANKS!
D
 
Last edited:
While doing so it tries to pump water into the system. But with both HW and heating valves off, there's nowhere to pump to, so the pressure rises, and it get's stuck into a loop of doing the same over and over again.

There should be a bypass of some sort in the pipework to prevent this from happening, usually an automatic bypass valve these days.

Your system will always continue to run the pump for a while after the demand for heating and/or hot water has gone off and the valves have closed. This is known as a pump overrun and is there to prevent excess heat building up in the boiler immediately after the burner goes off.
 

Reply to Heating Wiring Problem - cylinder thermostat not working in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
1K
I have a fully pumped Y plan heating system using a Potterton EP2 programmer. Drayton MA1 Diverter valve. I have just replaced the Actuator head...
Replies
4
Views
648
I have a Firebird oil boiler that is controlled by a Honeywell timer (no thermostat) that has channels for hot water and central heating...
Replies
8
Views
462
It has become a common occurrence that my boiler is failing to respond when the thermostat kicks in. I hear an audible click from the heatlink...
Replies
16
Views
2K
So a customer changed his own stat and wired it wrong and blew 3/4 fuses. Then heating was stuck on so I changed the programmer and this resolved...
Replies
10
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock