If you look at the side of the valves there's a manual override. When it's energised you will see it move. You can force it on by pushing it to the open position and holding it up while it tries to close on the spring.

If they are both operating as expected mechanically and you are getting voltage on the orange with the valve in the closed position you have a faulty auxiliary switch which might have been what the electrician was referring to.
 
one like this?

No, I wouldn't trust that anywhere near mains voltages.
 
I would remove the permanent live from the valves by disconnecting the orange from the top of 11 and move it to the spare of 5. The spare black looks like it goes to the boiler. I'd connect that to 5 in the junction box and connect the black to 3 in the boiler.
Thanks for the instructions!

Just to make sure I don't misunderstand please see photos below - can you please confirm?

Many thanks!

PXL_20220802_205109507.NIGHT_Original.jpg

PXL_20220805_141715708_Original.jpg
 
If you look at the side of the valves there's a manual override. When it's energised you will see it move. You can force it on by pushing it to the open position and holding it up while it tries to close on the spring.

If they are both operating as expected mechanically and you are getting voltage on the orange with the valve in the closed position you have a faulty auxiliary switch which might have been what the electrician was referring to.
Hmm 🤔
Apologies, but I don't seem to quite understand what to do..


First of all, have I understood the below correctly?

HW&Heating OFF > ZV are energised & therefore closed

HW&Heating ON > ZV are "loose" & therefore open


Should I manually open them while the HW&heating is OFF? And what should I do then? 🤔



Quick reminder
  • I was getting Voltage when HW&Heating is OFF (BEFORE changing the cables up according to your latest advice)
  • I've confirmed that when HW&Heating is ON that the pipes heat up next to both ZV - does this mean they work correctly?
    [*]Upon the advice from the sparky I had over, I recently had the HW ZV changed (though only the motor, no the pipe).



Sorry for the "barrage"..

Many thanks again!
 
In its rest position, a zone valve does not allow water to flow through it.
Applying 230V across the blue and brown wires opens the valve, so that water can flow, and also closes a switch between the orange and grey wires.
There is no electrical connection between the brown/blue wires and the orange/grey wires.
The power to the brown and blue wires should be controlled by the heating control system - thermostats, programmer, Nest, etc.
The boiler and pump should be controlled solely by the orange and grey wires, with no direct connection to the afore mentioned control system.
The boiler may also have a permanent live feed, which it uses to power the pump for a short while after the boiler has shut down, to prevent local overheating in the boiler.
 
In its rest position, a zone valve does not allow water to flow through it.
Applying 230V across the blue and brown wires opens the valve, so that water can flow, and also closes a switch between the orange and grey wires.
There is no electrical connection between the brown/blue wires and the orange/grey wires.
The power to the brown and blue wires should be controlled by the heating control system - thermostats, programmer, Nest, etc.
The boiler and pump should be controlled solely by the orange and grey wires, with no direct connection to the afore mentioned control system.
The boiler may also have a permanent live feed, which it uses to power the pump for a short while after the boiler has shut down, to prevent local overheating in the boiler.
Thank you for clarifying, Brian!! 👍👍👍

So I had it all wrong! 😂
 
OK, so

I followed Aaron's instructions - and the boiler still fires up immediately - with HW&heat OFF.

Then I check voltage to ZV's again

with HW&heat OFF > 244V

with HW&heat ON > 0V


Is it me, or should it be the other way around?? 😳
 
Before you go any further with this make sure you have the legionella prevention switched off in Nest settings as having this activated even with HW an CH in off boiler can kick in
 

Reply to Heating Wiring Problem - cylinder thermostat not working in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
1K
I have a fully pumped Y plan heating system using a Potterton EP2 programmer. Drayton MA1 Diverter valve. I have just replaced the Actuator head...
Replies
4
Views
655
m having a bit of an issue that is proving difficult to resolve. For 2 years I have been having no problems with my setup. I have a 3 zone house...
Replies
1
Views
1K
I have a Firebird oil boiler that is controlled by a Honeywell timer (no thermostat) that has channels for hot water and central heating...
Replies
8
Views
472
It has become a common occurrence that my boiler is failing to respond when the thermostat kicks in. I hear an audible click from the heatlink...
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock