Discuss Heatstrip THE3200r Trips Switch in the DIY Electrical Advice area at ElectriciansForums.net

Reaction score
0
Our sparky has just installed 2 x Heatstrip THE 3200 strip heaters (13A Max Each) which keep tripping the switches in the power board.

We have checked the cabling (20A Max Each) as well as the Power board (50A) to ensure capacity.
Reading the manual the guide recommends hardwiring the heaters as opposed to a plug and socket.
Could the fact that they have been wired via a plug and socket be causing them to trip, or is this a red herring?

Thanks in advance
 
what is tripping (MCB/RCD)? and what rating?photo would help.
 
You’ll have to excuse my ignorance but MCB
 

Attachments

  • 552199BE-2909-4AE4-AC26-9E11887E52CD.jpeg
    689.1 KB · Views: 5
can't tellfrom photo. what do they have on the front of the breakers. B16?
 

Reply to Heatstrip THE3200r Trips Switch in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
751
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Our family room is part of an addition built a few years ago. We had an issue with nuisance tripping on an AFCI and the electrician came and...
Replies
2
Views
1K
I'm not an electrician. I clean cookers and today arrived to a rangemaster range cooker. Got started, and as part of my routine, I turn on ovens...
Replies
1
Views
840
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock