brucelee
-
- Reaction score
- 691
HI all
I need some advice and guidance on a lower then expected IR on a New ring final circuit
when carrying out testing continuity was correct and so to the IR testing
I tested L-N >299 perfect
L-Cpc >299
N-Cpc > anywhere from 40M/ohms to 299
so as its new rewire I split in half at centre point and began trying to locate any damage trapped Neutrals in back box etc
as i was splitting and testing the reading began to rise
so i took all sockets of on the suspect side
all individual legs were 299
so started to reconnect 1 at a time conducting further Ir and as I got so far reading lowered
the readings are Fluctuating and if you hold the test button down readings rise
sometimes as low as 40+meg sometimes all the way upto to 299
I suspected new wet plaster or there is a socket in rear bedroom on rear wall and previously this wall had been damp or water damage due to plastic windows fitted in old wooden sash frames the wood has rotted so water had been penetrating and damaged the plaster on this wall when chasing all plaster on this wall under window fell off
anyway I cannot pinpoint the low reading to any individual socket or length of cable
as i suspected this socket and after trying locate for 5 hrs plus
thought wait for the plaster to dry as it was deep depth of plaster here
the plaster has now been done for over a week so should be dry
so tested again and still readings at ccu range from 40+ upto 299
I repeated half splitting method and still no joy when i disconnect neutrals and earths at sockets readings rise soon as i reconnect readings fall
without sockets screwed back
I know this may sound daft and dont know why i decided to try it but
I decided to test between the Neutral of the socket and the wall and got similar strange readings
so just meggered the wall lol and got very low reading of 0.05
the wall at the side 2 feet away i got 299
I then decided to check for any voltage present between sockets and any copper pipes under the boards nothing
I tested between line and the wall for voltage and got 131v??????
tested nearby wall from a High level TV socket on this wall and got 5v
tested the suspect socket and the nearby wall and got 5v
Do you think damage has occurred to cable from plaster or plumber
the wall maybe causing issues due to damp
any help on this would be truly grateful as its fried my head lol spent 10hrs in total trying to pin it down i even tried bypassing sockets with new lenght of cable from living room socket to rear bedroom
WISHING I HAD INSTALLED TWO RADIALS
ideas please
I need some advice and guidance on a lower then expected IR on a New ring final circuit
when carrying out testing continuity was correct and so to the IR testing
I tested L-N >299 perfect
L-Cpc >299
N-Cpc > anywhere from 40M/ohms to 299
so as its new rewire I split in half at centre point and began trying to locate any damage trapped Neutrals in back box etc
as i was splitting and testing the reading began to rise
so i took all sockets of on the suspect side
all individual legs were 299
so started to reconnect 1 at a time conducting further Ir and as I got so far reading lowered
the readings are Fluctuating and if you hold the test button down readings rise
sometimes as low as 40+meg sometimes all the way upto to 299
I suspected new wet plaster or there is a socket in rear bedroom on rear wall and previously this wall had been damp or water damage due to plastic windows fitted in old wooden sash frames the wood has rotted so water had been penetrating and damaged the plaster on this wall when chasing all plaster on this wall under window fell off
anyway I cannot pinpoint the low reading to any individual socket or length of cable
as i suspected this socket and after trying locate for 5 hrs plus
thought wait for the plaster to dry as it was deep depth of plaster here
the plaster has now been done for over a week so should be dry
so tested again and still readings at ccu range from 40+ upto 299
I repeated half splitting method and still no joy when i disconnect neutrals and earths at sockets readings rise soon as i reconnect readings fall
without sockets screwed back
I know this may sound daft and dont know why i decided to try it but
I decided to test between the Neutral of the socket and the wall and got similar strange readings
so just meggered the wall lol and got very low reading of 0.05
the wall at the side 2 feet away i got 299
I then decided to check for any voltage present between sockets and any copper pipes under the boards nothing
I tested between line and the wall for voltage and got 131v??????
tested nearby wall from a High level TV socket on this wall and got 5v
tested the suspect socket and the nearby wall and got 5v
Do you think damage has occurred to cable from plaster or plumber
the wall maybe causing issues due to damp
any help on this would be truly grateful as its fried my head lol spent 10hrs in total trying to pin it down i even tried bypassing sockets with new lenght of cable from living room socket to rear bedroom
WISHING I HAD INSTALLED TWO RADIALS
ideas please