Thanks again.

Good idea with the 45A connection points then a back box for either connecting a socket face or an fcu but another slight problem is that there is nowhere to put any switched items as the cupboards are boxed in floor to ceiling so only option would be to place inside the top cupboard above the ovens or quite a distance away else where in the kitchen. What do you think?

Just wanted assuring about the induction hob really as they have stated a 2.5mm cable but at 7Kw then adding a treble socket outlet (pop up socket) if this was used at 3Kw that's 10Kw minus any diversity so in excess of 40A as you said I suppose I've answered my own question. Oh the pop up is a good quality one at £165 trade but only using this as the island unit has nowhere to put any other socket outlets unless it's in a cupboard again as its Quartz stone straight on top of units unless anyone has alternative suggestions I'm screwed really.?

Many thanks

The regs require clearly identifiable and accessible. But then the IET don't design kitchens. Sometimes you have to put the isolators in the best place possible but not ideal. So with some kitchen designs that sometimes has to be in a cupboard. Just make sure it's accessible by people other than giants, and not behind wall unit
accessories. Think it would be better closer to an appliances in a cupboard, rather than 6 metres away in another room IMO.

Ditch the pop up and have some sockets on the floor units, just below the worktop. Pops up just get in the way, when 'popped up', and don't think they look particular nice IMO.

PS don't put the isolator above the appliance, not useful if it starts to catch fire, and adjacent cupboard is better IMO.
 
Just wanted assuring about the induction hob really as they have stated a 2.5mm cable but at 7Kw then adding a treble socket outlet (pop up socket) if this was used at 3Kw that's 10Kw minus any diversity so in excess of 40A as you said I suppose I've answered my own question.
Think you have your cals wrong. telectrix gave you a figure of 16amp, diversity cals suggest 5amp for single socket, so your pop up adds 15amps (if your using industrial kitchen appliances!). So that's 31amps? So 32 amp supply would be suitable, not allowing for route & vd if any.
 
I'd be checking with the manufacturer's connection data regarding all the appliances. They know what diversity, and how they have built that diversity into their appliances, and what size cable they require for safe operation. It is invariably always smaller cable than required for the stated FLC, but do check. I have connected full electric hobs with 1.5mm, 2.5mm, and 4.0mm cable. I have also connected appliances that have no built in diversity as confirmed through current measurement.

Which is why I always like to see the appliances on site and get the info from them rather than go on a kitchen plan or even brochures as they are sometimes not forthcoming with the correct info , don't go on what kitchen fitter tells you ....
 
if a kitchen fitter told me the sun rise in the east, i'd check before accepting it.
 
Thanks for the reply's again all very much appreciated.

I appreciate what you have said about the 2.5mm cable to the hob and 13A socket for the island but even with that diversity applied it would still be around the max carrying capacity and my mrs will have all 4 plates of that hob at full all at once on a regular occasion but in any case I'm sure not many of you would go for that size cable running at its max when you could just install a 4 or 6mm whilst undertaking the install and balls to the kitchen fitters drawing?

In ref to doing away with the pop up socket I'm screwed again really as the ends of the island are fitted with a cloaking panel which is the same high gloss finish as the cupboard doors so can't really make holes in it hence the pop up.

Would you all be happy with running the led cupboard lights off the appliance wiring say on a fused spur or whilst it's being wired just throw in a dedicated lighting supply?

Cheers Keith
 
Thanks for the reply's again all very much appreciated.

I appreciate what you have said about the 2.5mm cable to the hob and 13A socket for the island but even with that diversity applied it would still be around the max carrying capacity and my mrs will have all 4 plates of that hob at full all at once on a regular occasion but in any case I'm sure not many of you would go for that size cable running at its max when you could just install a 4 or 6mm whilst undertaking the install and balls to the kitchen fitters drawing?

In ref to doing away with the pop up socket I'm screwed again really as the ends of the island are fitted with a cloaking panel which is the same high gloss finish as the cupboard doors so can't really make holes in it hence the pop up.

Would you all be happy with running the led cupboard lights off the appliance wiring say on a fused spur or whilst it's being wired just throw in a dedicated lighting supply?

Cheers Keith

I don't think anyone has suggested using a 2.5mm cable for your hob? You should calculate the design current, using diversity and other correction factors, then select an appropriate sized cable & ocpd.

The suggestion of putting sockets on the floor units, just below worktops, is nothing new. Any decent kitchen fitter or electrician would be able to cut an aperture in high gloss décor panel for a back box? If there is insufficient room for a back box, I've used Click Mode 1G To 2G 16mm Deep Converter Pattress (CMA091) - https://www.electrical2go.co.uk/mode-1-gang-to-2-gang-16mm-deep-converter-pattress.html. However not designed for this purpose there is only sufficient space to terminate one cable.

In a new install, I prefer to switch lights from a light switch not an FCU. Don't know how many led lights you are installing, but you may need to consider in-rush current, if controlled by one switch.

From your replies, I'm wondering if you are competent enough to carry out this work and you suggest you are going to use a 3rd party to certify & notify this installation, no offence. You may wish to peruse this thread; Diy wiring extension - http://www.electriciansforums.co.uk/threads/diy-wiring-extension.113214/
 
Thanks for your reply Midwest.

I appreciate that no one suggested keeping the 2.5mm cable to the island to run the hob and socket but at the same time whilst advising me it was viable with diversity I was expecting some responses being alarmed like myself that they wanted me to install a cable from new that was going to run towards its maximum capacity on a daily basis. All I was after was after was reassurance I was correct in thinking the drawing was indeed inadequate or was at best not what professional electricians would recommend in their daily practice. As I undertaken my qualifications 30 years ago and then ending up working within the industry again a few years back and went and did all my C & G again and also did my 17th edition at the same time. We were an NICEIC registered company and I was the qualifying manager so I appreciate its not what I do day in and day out and I may of forgot some of the terminology but when I'm first fixing my own home I think my competence which is all that is required plus proof the installation meets part P (which 5 day sparks/ kitchen fitters can obtain) and because of these reasons I was simply asking people much more in the know than I am if it was in fact not recommended to wire in the way the kitchen company had recommended in their drawing. As for certificates and notification I am known by all my friends and family as the King of overkill and trust me this will be wired well in excess of what time and money normally allow, and will be certified and approved accordingly. Sorry if I worried or offended you or anyone else in asking for advice as I'm just second guessing myself when a company currently in business (although a kitchen company) are telling me this is how it's done everyday nowadays and it's my very incompetent self that immediately thinks this is inadequate.

I do really appreciate what you have said and have even swatted up on my onsite guide since receiving many of your reply's.

Many thanks again, Keith
 
Thanks for your reply Midwest.

As for certificates and notification I am known by all my friends and family as the King of overkill and trust me this will be wired well in excess of what time and money normally allow, and will be certified and approved accordingly. Sorry if I worried or offended you or anyone else in asking for advice as I'm just second guessing myself when a company currently in business (although a kitchen company) are telling me this is how it's done everyday nowadays and it's my very incompetent self that immediately thinks this is inadequate.
No offence meant, if your suitably qualified, then that's that.

As regards certification, I note that this work is being done as part of an approved planning application or Building Regs. You may wish to read the link I posted on a similar thread, about certification & notification. The subject comes up many times, and can cause complications, even for qualified electricians.
 

Reply to HELP...Kitchen wiring inadequacies??. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I am Currently in the process of building an extension and my builders will shortly be getting their electricians to commence the first fix...
Replies
6
Views
356
Hello All. I'm quite new to this game and gaining experience, but going well in the main. My customer wants to feed a Hob ( on island in centre...
Replies
5
Views
244
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
736
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
921
Hello everyone, I'd like to seek your input on a matter. I'm in the process of designing the electrical connections for the following kitchen...
Replies
38
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock