Discuss Help pleas!!!! in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

D

dannydore

Hi all. Been reading a lot of topics in regards to grouping factors, none of which seem to have the exact answer I'm looking for.


I'm currently in the process of doing a project for my 2396 Design & Verification course which is a 2 storey college block. I'm using metal trunking (method B) and pvc 70ºc singles (Table 4D1). There are 3 runs of trunking which encompass the whole building, 2 for the ground floor, and 1 which rises to the 1st floor. My grouping factors are 0.47 (11 circuits) for both of the ground floor runs, and 0.43 (14 circuits) for the 1st floor run.


After doing all of my Lighting circuits, I came to the Power calculations. Obviously, these grouping factors applied to a 20a Ib (or In) produces ridiculously high Iz (or It) figures (10mm to be precise).


"Use Note 9", I hear you say... Well, even after changing all of my lighting circuits to 2.5mm, only 6 circuits were lightly loaded (2 on each run) Thanks to the Guilds for making the majority of the lighting fluorescent/discharge with a 1.8 factor.


As the drawings merely show twin s/o's, I have no idea what the actual uses are for each circuit, and I would actually prefer to use the correct figures found in the Regs.


The only solution I can see is changing all of my containment to either add another trunking, or a completely different installation method. But seeing as I've had these all printed out on A1 scaled drawings, I'm a bit reluctant to do so. Also having worked on site for 4 years or so, I (and no doubt every other commercial/industrial spark) have seen trunking runs stuffed to the brim. Something just doesn't add up!


Am I missing something here, or can anybody suggest an alternative?


Thanks
Danny
 

Reply to Help pleas!!!! in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I have had my kitchen rewired and plastered. I have had a 6mm t+e on a dedicated 32a circuit for a 60cm electric cooker. In hindsight, had i known...
Replies
11
Views
576
Hi all, I have two questions regarding wiring and containment on commercial property stairwells in Ireland. We are currently wiring a 3 story...
Replies
10
Views
702
Recently moved into a house from the 70s. There's no ceiling light in the living room. Assuming the switch for the room was to one of the outlets...
Replies
1
Views
434
Hi All I would appreciate some help with a few questions here regarding cables sizing, I'm using the latest 18th edition, amendment 2. Q1...
Replies
0
Views
917
Hi all, I just found this forum last night and figured I would post my issue since I can't find much out there with a similar situation. My job...
Replies
4
Views
412

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock