Discuss Help with hall wiring in the The Welcome Forum area at ElectriciansForums.net

Reaction score
4
Hi I moved into my new flat and have had to decorate and repair so much, it had a tube light fixture in the kitchen (open plan living room and kitchen) fitted a ceiling rose no issue and have changed the 3 light switches to brushed stainless steel no issue I have changed all the plug sockets to match no issue. Just finished the hall decorating so gone to do the same and like a numpty before I started to take it apart I didnt take a picture and cannot get both switches to work. 1st switch is a single switch which controls the light in the hall second switch is 2 gang and controls the hall and bathroom light I'll post pictures strangely I can only find 1 live wire!! Please can someone help I'm close to rubbing my eyes on a pebble dashed wall!! Below is the wiring the 4 wires is for the 2 gang switch and the 3 wire for the normal switch and at the bottom are the switches I want to replace the originals with but cant even get the original switches to work properly what do I do? Oh the power is switched off to the light switches btw. I know once someone says it I'll be kicking myself I have mental healt problems and took this on whilst I can't concentrate properly
 

Attachments

  • 20200523_202503.jpg
    88.5 KB · Views: 48
  • 20200523_202503.jpg
    88.5 KB · Views: 50
  • 20200523_201918.jpg
    66.8 KB · Views: 50
  • 20200523_202312.jpg
    156.2 KB · Views: 50
  • 20200523_201936.jpg
    55.4 KB · Views: 45
  • 20200523_202005.jpg
    64.9 KB · Views: 39
  • 20200523_202025.jpg
    69.4 KB · Views: 43
Unfortunately there are so many different ways for lights to be wired it would be a stab in the dark for any of us to advise.
Maybe one of the members is local to you?

for clarity. Can you confirm the 2 gang switch controls bathroom and hall, the 1 gang just the hall? The hall light controlled at 2 switches.
 
Picture number 3 doesn’t look right to me - it looks like the live link feed for the second light so should be linked from one switch to the other and permanent live goes into one of those so your supply live can feed both switches. All the cables should be marked as live too as they will all be live feeds or switched lives or strappers
 
Unfortunately there are so many different ways for lights to be wired it would be a stab in the dark for any of us to advise.
Maybe one of the members is local to you?

for clarity. Can you confirm the 2 gang switch controls bathroom and hall, the 1 gang just the hall? The hall light controlled at 2 switches.
Yes The hall as a 1 gang outside the living room door and the 2 gang is at the front door which controls the bathroom light and kitchen. I asked my grandad to come have a look for me but he won't I know its something so simple I just can't focus enough at the moment. I just can't believe I didnt take a picture I always take a picture ?‍♂️
[automerge]1590310386[/automerge]
Yes The hall as a 1 gang outside the living room door and the 2 gang is at the front door which controls the bathroom light and bathroom. I asked my grandad to come have a look for me but he won't I know its something so simple I just can't focus enough at the moment. I just can't believe I didnt take a picture I always take a picture ?‍♂️
[automerge]1590310498[/automerge]
Picture number 3 doesn’t look right to me - it looks like the live link feed for the second light so should be linked from one switch to the other and permanent live goes into one of those so your supply live can feed both switches. All the cables should be marked as live too as they will all be live feeds or switched lives or strappers
That light switch I didn't touch that bridge so that's where it was
[automerge]1590310581[/automerge]
Yes The hall as a 1 gang outside the living room door and the 2 gang is at the front door which controls the bathroom light and kitchen. I asked my grandad to come have a look for me but he won't I know its something so simple I just can't focus enough at the moment. I just can't believe I didnt take a picture I always take a picture ?‍♂️
[automerge]1590310386[/automerge]

[automerge]1590310498[/automerge]

That light switch I didn't touch that bridge so that's where it was also the other black wire did have red tape on its fallen off got some coming as its regulatory to have the switched live marked
 
It is pretty hard without being able to test things!

I suspect the one with 2*red and 1*black you will find that one red/black pair is a T&E running to the double switch, and they would go to the L1/L2 terminals of one half of the double switch, and to the L1/L2 of the single switch.

On the double switch the common of both halves there ought to have the red link wire and go to your "permanent live" red.

That would leave the remaining black (maybe "bathroom switched live") of the double switch to go to L1 (probably) of the other switch. Or L2 if it works upside-down!

And the 3-wire set would have the lone red going to C (common) of the single switch.

But that is simply a guess!
 
Ah.. ok... your original post said both switch positions controlled the hall, which i assumed meant it was a 2 way switch.

If all the switches are normal 1 way.... disregard the terminals marked as 2 way... you dont need them.

That just leaves you with Commons (for the lives) and 1way terminals... for the switch wires.

The 2 gang switch is essentially 2 separate switches, so will need a link between the 2 commons... Where the link is just now doesnt make sense.
 
Ah.. ok... your original post said both switch positions controlled the hall, which i assumed meant it was a 2 way switch.

If all the switches are normal 1 way.... disregard the terminals marked as 2 way... you dont need them.

That just leaves you with Commons (for the lives) and 1way terminals... for the switch wires.

The 2 gang switch is essentially 2 separate switches, so will need a link between the 2 commons... Where the link is just now doesnt make sense.
I know that's what I thought the link should go to the other common with the single permanent live going in the common point
[automerge]1590312719[/automerge]
As above is that where the link was in the original setup or have you put that there??
No the link is untouched
 
i could sort you that in under 1 hour. butPreston is a tad far for me. maybe a forum member is closer and can help.
 
if you look at the other 2 way switch that uou've not touched??? see how the cable/s is/are connected. then the other end of the cable/s should match up the same.
 
if you look at the other 2 way switch that uou've not touched??? see how the cable/s is/are connected. then the other end of the cable/s should match up the same.
There isn't another 2 way I didn't touch oh the picture artistically drew is the new switches the old white I took off the wall and that is where the link is I just can't understand why the link would go from com to 3 so I'm working the 2gang as 2 separate switches which if I'm right it should work yes?
 
Regarding your new drawing....No.... Without getting too close to a "step by step" instructions which is frowned upon....

Ignore the 2ways. you don't need them.

Can you remember how the lights were connected? If it was 3plate, or loop in... there seems to be an extra red at the single switch.?

The commons will need the perm live into them.... the switch wires coming out of the one ways...
You could possibly work out the single gang switch no problem.

I think its been mentioned before, but all you have here is lives and switched lives... there's no neutral that could cause a short circuit... so might be a case of trial and error until you get the right configuration. (assuming the lights have been reconnected properly)

Another thought here.... Are all the lights on the same circuit? or have you maybe got 2 feeds into one switch box, which could be dangerous if the 2 circuits become interconnected
 
and this works the way you want it to?

Im worried where the reds into 2way are going

Also, you need to link the metal faceplates to the back boxes with a little green/yellow to earth them.
It works just as before both hall switches independently on and off and bathroom on the other switch in the 2 gang working also the switch plates already have the earth in there should of shown that really
[automerge]1590317544[/automerge]
It works just as before both hall switches independently on and off and bathroom on the other switch in the 2 gang working also the switch plates already have the earth in there should of shown that really
Also the 2 reds are the link in COM as they are the perm live all lights in the flat work and I haven't electrocuted myself so win win haha I've only got 2 switches to change now and they are simple that one just threw me off
 
image-jpg.58357
Bit of a rough drawing but this is how it should be wired,ensure all the wires are identified as live using red tape and the single hallway switch should have the com terminal going directly to the light. The 1 way wire should terminate on the second single switch to that 1 way wire - the same for the 2 way terminal as in the drawing.
The com terminals in the double switch should link Together and the permanent live also terminates into one of these.
As mentioned, ensure the switches are earthed to the back box which should be earthed already and that this wire is identified with green and yellow sleeve or tape
 

Attachments

  • image.jpg
    107 KB · Views: 50
image-jpg.58357
Bit of a rough drawing but this is how it should be wired,ensure all the wires are identified as live using red tape and the single hallway switch should have the com terminal going directly to the light. The 1 way wire should terminate on the second single switch to that 1 way wire - the same for the 2 way terminal as in the drawing.
The com terminals in the double switch should link Together and the permanent live also terminates into one of these.
As mentioned, ensure the switches are earthed to the back box which should be earthed already and that this wire is identified with green and yellow sleeve or tape
Yeah this is what I've done just couldn't understand that link it was in the wrong place all together but it's all neat and tidy and now marked with the correct tape and the earths were fine didnt need to touch them
 

Reply to Help with hall wiring in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hello, I'm replacing standard light switches in my hall and landing with touch switches (not smart, just touch on/off) like these from Amazon...
Replies
7
Views
610
Hi, I’m looking to install 3 meross smart switches for 3 lights: entrance switch: only 1 gang but 3 way switch bedroom switch: 2 gang (1 is 1...
Replies
9
Views
347
Hi all, currently doing a job at a house where there are 3 switches In the hallway to control the hall lights. All 1 gang switches, one at...
Replies
2
Views
539
Hi I am trying to replace my old white light switches for nice chrome ones but the wires are all red but the new switch has only l1 l2 top and...
Replies
6
Views
685
I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
446

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock