    I live in a flat in Leeds and am needing some advice.

    I have one extractor fan that connects to two bathrooms (Call them A and B). The switching on of a light for either should turn the fan on. Also in the kitchen there is a switch incase we need to turn it on there too. There is a ceiling vents in each of the three rooms. We are like 99.9% sure this is how it worked when we moved in.

    However since then we have changed the switch (Lets call this bathroom A) for a chrome one and now whenever we turn the switch on in Bathroom B it turns the light on in both Bathroom A and B. The fan also comes on like it should.

    Bathroom A switch just turns on A's Light and also the fan.

    We have spoken to an electrician and he said that the light switch to bathroom A must of been a switch with 2 switches on it (2 gang is it?) Both me and my partner are 99.9% sure that this wasn't the case though.

    Can anyone confirm what we need to do and if it is at all possible to have only one switch work each rooms light and the fan. We really wish we had kept the other switch however we didn't know it was a problem as we didn't use bathroom B much so didn't notice the issue of the light coming on in A and B when you press B's switch.

    Any advice would be greatly received. And if you need me to clarify anything or take pictures then just let me know.

    Matthew
     
  2. Archy Styrigg
    Offline

    Archy Styrigg Forum Mentor

    Location:
    Manchester
    Ah, that'll be the double pole light switch affair.
    I did have a diagram somewhere ...
     
    • Agree Agree x 2
    • Like Like x 1
  3. buzzlightyear
    Offline

    buzzlightyear please let me back in to the prison cell. Electrician's Arms

    Location:
    star command
    pm him .
     
  4. mattleeds
    Offline

    mattleeds EF Member

    Location:
    Leeds
    Ahh thanks I will do that sounds promising :D Very excited.
     
  5. mattleeds
    Offline

    mattleeds EF Member

    Location:
    Leeds
    PM'd can't wait to see the answer :D i've been pulling my hair out over this!
     
  6. Leesparkykent
    Offline

    Leesparkykent Super Moderator Staff Member Super Moderator

    Location:
    Kent
    Double pole switch. 1 pole switches the fan, the other pole switches the light.
     
    • Like Like x 1
  7. Dazza1976
    Offline

    Dazza1976 Regular EF Member

    Yes as Archy mentioned, a double pole switch is required for this setup, not a 2 gang switch like you were wrongly informed. I have worked in quite a few new build properties that are wired like this, and a double pole switch is necessary to avoid the problem you have encountered. Have a look where you bought the switch from and see if they do that range in a double pole version, normally they are rated with higher Amp rating but still fine to use.
    The Only problem you might have now is wiring up the correct switch properly when you get one !
     
    • Like Like x 1
  8. Archy Styrigg
    Offline

    Archy Styrigg Forum Mentor

    Location:
    Manchester
    Found it!

    It's a bit rough like, but you'll get the drift :)

    fanwith3lights 001.jpg
     
    • Like Like x 1
  9. mattleeds
    Offline

    mattleeds EF Member

    Location:
    Leeds
    Ahh thanks sooo much! So is it a double pole on both bathrooms?
     
  10. Sintra
    Offline

    Sintra The Innkeeper Staff Member

    Location:
    Belfast/London
    Yes they will both need to be double pole. Also be sure to safely isolate the circuit at the source as turning on the other switch will make the common fan switched feed live.
     
    • Like Like x 1
  11. mattleeds
    Offline

    mattleeds EF Member

    Location:
    Leeds
    Thanks guys I have ordered some today. Hopefully will arrive tomorrow so i can fit them. Not cheap on amazon the Schneider Ultimate screwless for double pole! Will let you know how I get on.

    Many thanks again!
     
    • Like Like x 1
Loading...
Similar Threads - Help Wiring Switches Forum Date
Lighting help (wiring) Electrical Forum Mar 11, 2019
Wiring for waste pump help Electrical Forum Mar 9, 2019

Share This Page

Users found this page by searching for:

  1. wiring an extractor fan to 2 switches

Electricians Directory Post a Domestic Job Post a Commercial Job