Discuss Hi all having problems with this heating system will hw stick on because of power on terminal? in the Central Heating Systems area at ElectriciansForums.net

your wiring diagram doesn't make sense to me for a 2 port valve. A 2 port valve is simply an open and shut valve. It has the following wiring
Blue - neutral
green and yellow - earth
grey - permanent live
brown - switched live from thermostat (be it C/H or Hot water)
orange - switched live out to boiler.

The valve is normally closed and opens when it gets a switched live to the brown. When it opens a micro switch inside connects grey to orange which signals the boiler to fire.

How is your myson wired at moment
 
Cheers lads but there is no valve on hw (if there was it would solve it)
There is no cylinder stat either
(Called out just to put room stat on system)
Need hw only for summer when room stat isn't calling for heat
Thanks for input

Still wouldn't solve it correctly, you need a zone valve to open/close the primary to the cylinder coil and a cylinder stat to regulate the temperature of the hot water. Regulating it on the boiler stat is not the way to do it.

Work with a wet pants to upgrade it to an S plan.
 
It must be gravity hot water then eg no pump and 28mm pipes

So

Hot water
Prog (hot water)
Boiler

Heating
Prog (heating)
Room stat
Pump and boiler
 

Reply to Hi all having problems with this heating system will hw stick on because of power on terminal? in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

(Or that might be should a failed HW valve keep boiler running) Woke up this morning to find the boiler still running even though all timers off...
Replies
4
Views
1K
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
941
Hello , I’m trying to further my knowledge into UFH/Rad/HW valves heating systems with air source pumps. What is normally needed outside with...
Replies
0
Views
596
I have a fully pumped Y plan heating system using a Potterton EP2 programmer. Drayton MA1 Diverter valve. I have just replaced the Actuator head...
Replies
4
Views
618
I'm in Raleigh, North Carolina and have a well for my house's water supply. For some reason, pitless adapters, which allow all piping to be run...
Replies
1
Views
292

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock